RX3i Loss of I/O Module Error

LMBrian

Member
Join Date
Sep 2012
Location
Florida
Posts
54
Hi All,

From time to time we get this error on our system and in the I/O fault table it points to Slot 3 which has the HSC module in it, (IC695HSC304). Is there a fault handler or something along those lines that I can modify to 'avoid' this fault? It lasts for just 2 seconds and is followed by Module Fault and Add'n of I/O module all within the 2 seconds window. The result of this is that it gives an incorrect process distance reading on our process and has to be re calibrated.

TIA
 
The "Loss of I/O Module" fault indicates that the CPU has lost backplane communication with the HSC module. The "Addition of I/O module fault indicates backplane communication was restored.

It could be a bad connection between the module and the backplane. Check for bent pins on the module.

It could be a power supply problem. Check your Proficy Machine Edition file for the power supply loading.

I would also suggest opening a case with GEIP support. The Rx3I had problems with the expansion bus transmitter module where the location of the circuit board in the plastic case prevented a solid connection to the backplane. I don't know if there were similar problems with the HSC module, but it's a question worth asking.
 
Thank you Steve,

I will open a case with GE support as this issue pops up on different sites. The PS loading looks good and is just using 56%. Appreciate your feedback!
 
This is the feedback I received from GE to update anyone that may come across the same issue:

This sounds like a noise problem, but there are a couple of other easy things to check as well. I would start by checking the backplane connectors on the counter module and the power supply for bent/recessed pins. Make sure the backplane is solidly grounded.

I suspect the real problem is noise coming in on the field wiring, causing the module to reset. Make sure your signals cables are shielded and grounded. Try to separate them from high-voltage/noisy wiring. You may need to put ferrite beads on the sensor wiring.
 

Similar Topics

Hey guys, I'm on site integrating for the first day on a project where I'm programming RX3i (CPU 305) controllers and have hit a snag. At the...
Replies
2
Views
2,404
I have a system using Rx3I CRU320 redundant CPU with Proficy Machine Edition Software. In the hardware configuration of each CPU module, under...
Replies
14
Views
384
Hi, we are using Rx3i CRU320 redundant PLC system and we noticed a discrepancy between Primary and Secondary controller. Couple of variables (DI)...
Replies
8
Views
278
Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
Replies
5
Views
100
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
Replies
1
Views
969
Back
Top Bottom