Hi all,
I've got an SEW device I'm trying to set up to talk to a ControlLogix. I've used this exact combination before and everything has worked swimmingly, but for some reason this time the thing just won't talk!
I've got a managed switch so I set up port mirroring on the PLC port and ran a wireshark trace, filtered to the IP of the offending device. I'm seeing some traffic, but it definitely looks like just a "are you there?" "no, go away" type exchange. I don't have a lot of experience with interpreting wireshark and wondered if a kind soul with more knowledge that I would be able to have a quick look and help me out? I've attached a screenshot and the wireshark file.
Key points:
- Device is set up as a generic ethernet module
- Checked (and double/triple checked) assembly instances/sizes, IP address, data type, etc. All copied and the same as a working example at another site
- I have two identical units both behaving the same way, which mostly rules out a dodgy device issue
- While online with the PLC I can ping the device (and use the SEW software to go online to it)
- I have tried linking everything together with an unmanaged switch to eliminate managed switch issues - same results
- 1756-L71 with v23 firmware, via 1756-EN2T (working example at other site is 1756-ENBT, but surely not a factor???)
- Error code for connection is (Code:16#0204) Connection Request Error: Connection request timed out
- Not using Unicast, RPI is 10ms (changing this has had no effect - and again, that's the same as the working setup elsewhere)
Thanks in advance to anyone who's able to shed light on this!
I've got an SEW device I'm trying to set up to talk to a ControlLogix. I've used this exact combination before and everything has worked swimmingly, but for some reason this time the thing just won't talk!
I've got a managed switch so I set up port mirroring on the PLC port and ran a wireshark trace, filtered to the IP of the offending device. I'm seeing some traffic, but it definitely looks like just a "are you there?" "no, go away" type exchange. I don't have a lot of experience with interpreting wireshark and wondered if a kind soul with more knowledge that I would be able to have a quick look and help me out? I've attached a screenshot and the wireshark file.
Key points:
- Device is set up as a generic ethernet module
- Checked (and double/triple checked) assembly instances/sizes, IP address, data type, etc. All copied and the same as a working example at another site
- I have two identical units both behaving the same way, which mostly rules out a dodgy device issue
- While online with the PLC I can ping the device (and use the SEW software to go online to it)
- I have tried linking everything together with an unmanaged switch to eliminate managed switch issues - same results
- 1756-L71 with v23 firmware, via 1756-EN2T (working example at other site is 1756-ENBT, but surely not a factor???)
- Error code for connection is (Code:16#0204) Connection Request Error: Connection request timed out
- Not using Unicast, RPI is 10ms (changing this has had no effect - and again, that's the same as the working setup elsewhere)
Thanks in advance to anyone who's able to shed light on this!