How do I choose between Isolated and non Isolated analog modules? Where would I use one or the other and why. Need to add some analog outs to a small 1756 system and not sure what to look at.
 
If you need isolated inputs and outputs, you need an isolated module. If you don't need isolated I/O, you don't need an isolated module.

Put another way: If you can tie the commons of different things together without seeing a big flash and a puff of smoke, you probably don't need isolation. If there is a big flash and smoke, you do.

Isolation can also be used to break up ground loops, if there is that problem.

Honestly, if I need isolation, much prefer to use an isolator external to the PLC. That way, in the future, someone stumbling along in the cabinet has less chance of just moving the wires to a different module/output as a troubleshooting step and releasing the flash/smoke.
 
If you need isolated inputs and outputs, you need an isolated module. If you don't need isolated I/O, you don't need an isolated module.

Put another way: If you can tie the commons of different things together without seeing a big flash and a puff of smoke, you probably don't need isolation. If there is a big flash and smoke, you do.

Isolation can also be used to break up ground loops, if there is that problem.

Honestly, if I need isolation, much prefer to use an isolator external to the PLC. That way, in the future, someone stumbling along in the cabinet has less chance of just moving the wires to a different module/output as a troubleshooting step and releasing the flash/smoke.

Also, if there is mix of active and passive devices, best to put on isolated ins/outs
 
Hopefully my previous experience will help. I think you need to know what the device receiving the analog output signal is referencing that signal to. If all of the devices reference the signals to same ground as your analog module, then non-isolated is fine.

I recently had a non-isolated analog input module receiving signals from various devices. One of the devices was powered from a separate 120VAC source and it generated a signal which was referenced to some odd voltage (like 7VDC?) rather than ground. I needed a signal isolator for that input to keep things happy. Without the isolation, my ground reference probably would've been bouncing all over the place causing havoc.
 
What is meant by active / passive in terms of analog output type devices?

An active analog device is one that has its own internal power supply, there fore the signal is powered.

A passive device requires external power . Connecting multiple passive devices to the same analog input rarely causes issues as the power source is common for all if the power is supplied from the PLC panel. Most pressure and level sensors are passive.

Active devices can be flowmeters, PH analyzers usually all powered by AC.
 
Maybe I'm hijacking this thread but this happens to me recently:
I ordered a HART Flex I/O board 1794-IE8H, channels on this board are not isolated and I have 8 isolated 4-wires HART flowmeters. 1794-IE8H only works with non isolated HART devices. I have to order a 1794-IF8IH, channels on this are isolated and now all my flowmeters HART data is present and working properly.
 
How do I choose between Isolated and non Isolated analog modules? Where would I use one or the other and why. Need to add some analog outs to a small 1756 system and not sure what to look at.

Boils down to cost - I would always use isolated modules...
 
I always use isolated modules. Saves worrying about which devices are on which modules, headaches when the devices that show up on the machine are different than they were supposed to be, and allows some flexibility when you need to do something weird like run the same analog through two different supplier's PLCs.

the m340 8 channel isolated analog input module is ~$800 CAD I think? cost savings on the non isolated module can't be more than a couple hundred bucks, only takes one whoops to eat that up
 

Similar Topics

Hi All, First off, thanks for all the previous help. Now I have another question. I am using a 1756-OF8 to send a 0-10V signal to an...
Replies
6
Views
7,562
Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
Replies
4
Views
1,201
Good evening, just a dump question, I’ve configured channel no 13 with scalling as attached, then shown not linear reading, even when i simulate...
Replies
6
Views
1,705
Hello! I am trying to wrap my head around how to wire a 4-20mA sensor to my AB 1756 ControlLogix IF8 Analog Input card. Could someone educate me...
Replies
3
Views
3,757
Hello, I have a flow meter that has been in service for a few years now. I have recently noticed that my registration on the mag meter does not...
Replies
0
Views
1,121
Back
Top Bottom