I am doing a CompactLogix system with no CPU, it is a remote rack.
The PLC with the CPU is in a different room and the customer is doing the logic.

The customer wants to use Ethernet/IP.
What additional modules would I need to communicate from my remote rack to the PLC over Ethernet/IP?

Would it be either the 1768-ENBT or EWEB?
 
Last edited:
NetNathan,

I think you are a bit unsure as to what the 1768 communications interface modules can do for you?...

The 1768-ENBT is a complimentary EtherNet/IP communications interface that can only be used with the 1769-L4x controllers. It allows the local processor to communicate with other devices for control of I/O, produce/consume, connecting to a HMI, programming and diagnostics via the built-in web server.

The 1768-EWEB similarly must have a local 1769-L4x controller present. It supports bridging and routing, messaging, open sockets, customer web pages, programming and diagnostics via the built-in enhanced web server.

So you would have to use a 1769-L4x processor with a 1768-ENBT, just to use the CompactLogix platform as a "remote rack" over EtherNet/IP. Ownership of any I/O modules, of course here, does not belong to the "other" PLC.

I think you meant the 1769-AENTR?

This will allow you to use the CompactLogix platform as a standalone remote I/O rack.

Here's a link to some info...

http://literature.rockwellautomation.com/idc/groups/literature/documents/pp/1769-pp013_-en-p.pdf

Regards,
George
 
Last edited:
I ran into the 1769-AENTR when I was researching communication options for the CompactLogix.
Yet, I was confused because I thought the part number was for Point IO....but that is 1734-AENTR.

That is why I posted....thanks for the clarification..
 
NetNathan said:
I ran into the 1769-AENTR when I was researching communication options for the CompactLogix.
Yet, I was confused because I thought the part number was for Point IO....but that is 1734-AENTR...

When you're staring at those catalog numbers for enough years you get to know what family they belong to at a glance. I would always know 1769 products to be of the CompactLogix family in an instance, but the 1794 Flex I/O and 1734 Point I/O are certainly two that can be mixed up quite easily if your reading through information more quickly.

A small but important correction to my post. I mentioned the 1769-L4x controllers but that should have been 1768-L4x controllers. These controllers provide a second and separate 1768 backplane to the standard 1769 backplane on the opposite side of the processor. This is where the likes of the 1768-ENBT must reside. Without the presence of a 1768-L4x processor, the 1768-ENBT cannot gain access to the I/O data on the 1769 backplane, or CompactBus.

The 1769-AENTR communications adapter provides its own access directly to the 1769 backplane and so does not require a local processor to be present.

JeremyM said:
Which 1769 controller is deployed?...

Just a small point on your certainties here...

The controller may or may not be a 1769 CompactLogix. It just has to be EtherNet/IP compatible. It could be a 1756 ControlLogix or even another brand.

I'm not saying that you are wrong. It would be my first guess too. I'm saying that just because NetNathan is looking to use a distributed 1769 I/O rack, does not automatically mean that the customer's controller must also be a 1769 CompactLogix.

I'm just opening your mind to other possibilities here, that's all.

Regards,
George
 
I only ask to clarify connection count required versus what's available per the controller.

I did mis-write my question - probably better to use "CompactLogix"...
 
JeremyM,

Okay. I understand where you are coming from, and you are right to consider the Connections count, but I still feel you may be missing my basic point.

I'm only pointing this out to you because I notice how you are thinking about this in a certain way, when it is not as cut-and-dry as you appear to think it is...

JeremyM said:
...I did mis-write my question - probably better to use "CompactLogix"...

That would be the same difference my friend...

Whether you used "1769", "CompactLogix", or "1769 CompactLogix", etc., the possibility that it may not be a CompactLogix, at all, still remains.

It would be more correct to have simply asked...

"Which controller is deployed?"

The core misconception I feel you may have here is that you are thinking that because the EtherNet/IP distributed I/O is intended to be of the 1769 CompactLogix family then the owner controller must automatically be of the same 1769 CompactLogix family. It does not automatically mean that.

So my point is that you, if knowing better, should not automatically assume it to be a CompactLogix controller, at all. Even though, and as I said I would also have guessed, it is highly likely that it may be.

Rock bottom point...

EtherNet/IP is an open standard. Realize that there are other controllers which may communicate with a 1769-AENTR over EtherNet/IP, other than the same 1769 family controllers.

Also, while I'm being my usual picky self...

"How many and what kind of remote I/O are planned?

Notice how I used the term "distributed I/O" above?...

For Allen Bradley/Rockwell, where one is not specifically dealing with "remote I/O", I would always refer to it as "distributed I/O", simply because remote I/O is a very specific type of legacy I/O for this brand. Because we know this is intended to be a non-local EtherNet/IP I/O rack, it would more correctly be referred to as distributed I/O, rather than remote I/O.

So it would have been more correct to have asked...

"How many and what kind of distributed I/O are planned?"

Again, I'm being quite picky here, I know. But I always try to correct what I perceive to be a misconception or a misuse of certain specific terms.

Recently I've mentioned as such for the "slight" misuse of the the terms "multistate indicator", the abbreviated "RSLinx", and would you know, the incorrect term of "1769-L4x" instead of "1768-L4x", which of course I was guilty of above.

That is just to point out that it is in my nature to try to correct these subtle mistakes, when and where I see them, even when they are my own, in the interest of education, more so than trying to be a "know-it-all", of which I am most certainly not.

In other words, please do not take the above the wrong way. It is intended to be constructive criticism.

On the point of Connections...

The 1769-AENTR adapter has a limit of 96 TCP/IP Connections, or physical devices that can be connected to it's Ethernet port. This should be more than sufficient for most applications.

Note: You can configure the adapter to communicate with one controller using an exclusive Owner Connection, or Listen Only Connection, depending on the I/O modules used. You cannot use both together. So only one controller can communicate with the adapter using Class 1 Connections at any given time. If another controller requires the same I/O data then you would have to use the Produce/Consume model or implement Explicit Class 3 Messaging. This is only important if you are adding an 1769 EtherNet/IP distributed I/O rack to a busy network that requires the simultaneous distribution of the multicast I/O data to more than one controller.

The limit on the maximum number of I/O modules under the adapter is 30 across 3 racks. This is because the adapter has a limit of 30 Class 1 CIP Connections. This facilitates the use of up to 30 Direct Connections from the controller to the individual I/O modules.

You cannot use a Rack Optimized Connection from the controller to this adapter for all 30 I/O modules. You must use separate Direct Connections.

The adapter also supports up to 32 Class 3 Explicit Messages to the I/O modules.

It also has an I/O packet rate of 10,000 pps (packets per second)

NetNathan,

This adapter "should" be more than capable, Connection-wise, at your end. But as we don't know the intended controller to be used on the customer's side, the controller's TCP/IP and CIP Connection limits or currently available Connections "could" have a bearing on the success or failure of this project, as JeremyM so rightly points out.

Whether you feel that this is important to you or you see it as being their problem, is up to you, but if you want the project to go smoothly, I would advise you to take it into consideration.

Regards,
George
 
Last edited:

Similar Topics

I am designing a system that will have about 30 modules total. My question is when I daisy chain from the 1st chassis to the 2nd do I call it rack...
Replies
4
Views
4,258
The manuals specify that the controller's "power supply distance" is a maximum of 4 modules. Does that mean that there can be 4 modules between...
Replies
0
Views
4,182
Hi everyone, i have a compact logic 1769-L18 PLC and I'm using FTalk View ME for the display. I wanted to do some visualization on Grafana. At...
Replies
1
Views
95
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
98
Does this instruction calculate values during a single scan, or does it require number of scans based on element count in the array? For Example...
Replies
3
Views
113
Back
Top Bottom