eta537 Member E Join Date Jul 2013 Location St. Louis Posts 3 Nov 5, 2015 #1 Looking for a way to verify Tag Usage or IO usage in RSlogix 5000 based on cards configured? I am used to using PLC 5 where you can use the usage option in data tables to verify what I/O is used throughout the PLC logic. Thanks
Looking for a way to verify Tag Usage or IO usage in RSlogix 5000 based on cards configured? I am used to using PLC 5 where you can use the usage option in data tables to verify what I/O is used throughout the PLC logic. Thanks
rdrast Lifetime Supporting Member Join Date Apr 2003 Location South Carolina Lowcountry Posts 5,544 Nov 5, 2015 #2 Generate a cross reference on the module in the controller tags browser. Ex: Local:1:I