Modbus RTU connection from a Micrologix 1400 to Accuvim iiR-D

sophickj

Member
Join Date
Nov 2015
Location
Jamaica
Posts
9
Hi,

I need some assistance in establishing a modbus RTU connection (communication) with a Micrologix 1400 and a accuvim ii. An AIC was used to connect from the accuvim ii to the PLC but I am not getting a connection. Anyone familiar with this process can assist please.
 
The 1761-AIC+ is a RS232 to RS485 converter/isolator and a point to point RS232 isolator. See manual below (page 10). It will work for the OP's application.

https://www.google.com/url?sa=t&rct...S6EO3n7Y_amsAQaQg&sig2=4WAlI984E3LCm5t7DzPAmQ

But channel 0 can be setup for RS485 communication without using an AIC, see excerpt from the manual for the ML1400 below.

When connecting to RS-485 network using DH-485, DF1 Half-Duplex Master/Slave,
Modbus RTU Master/Slave or DNP3 Slave protocols, the MicroLogix 1400 can be
connected directly via Channel 0 without an Advanced Interface Converter, catalog
number 1761-NET-AIC. The Channel 0 combo port provides both RS-232 and
RS-485 isolated connections. The appropriate electrical interface is selected through
your choice of communication cable. The existing MicroLogix 1761 communication
cables provide an interface to the RS-232 drivers. The 1763-NC01 cable provides an
interface to the RS-485 drivers.

I am not familiar with the OP's Accuvim iiR-D
 
Last edited:

Similar Topics

Just working on a job with a heap of Schneider power monitors connected to my PLC with Modbus RTU. There are the usual D0 and D1 connections...
Replies
4
Views
2,231
Hi! Greetings, I've been trying to use the PLC M221 to control and read the variables from the VSD ATV312 through Modbus RTU, which is something...
Replies
2
Views
1,601
Hello, I'm a newbie to PLC's and network protocols, and I need your help with setting up a modbus rtu network. Hardware 1: Micrologix 1400...
Replies
8
Views
12,168
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
Replies
1
Views
40
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
6
Views
135
Back
Top Bottom