Micrologix 1200 to PanelView plus 400 via 1761-net-aic

Mister Mac

Member
Join Date
May 2013
Location
Longford
Posts
19
Hello all,

I am having an issue at a clients site whereby a loss of comms between a PV400 and a micrologix 1200 has occurred.
The PV is connected to a 1761-net-aic via the RS-232 port through a null modem adapter into the RS-232 (8-pin mini-DIN) com port of the AIC.
5 AIC's are in the 485 network with the micrologix 1200 connected into the RS-232 (8-pin mini-DIN)of one of them.
The runtime path in the FTView application is set to a 485 serial driver with the micrologix 1200 device as a child.
Should there be another driver that communicates with the 1761-net-aic configured in the runtime path?

Any suggestions appreciated
 
Hi,

The 1761-NET-AIC is an Advanced Interface Converter. Its purpose is merely to convert RS-232 electrical signals to RS-485 electrical signals.

It also provides electrical isolation between all three of its ports.

It does not require a driver, specific to it, to establish communications through it from a controller to a PanelView terminal.

The MicroLogix 1200 port is configured for the DH-485 protocol, as is the PanelView Plus 400's port and they are both connected to the RS-232 (8-pin Mini-DIN) port 2 on their adjacent AICs.

The 1761-NET-AIC, using its port 3 (6-pin phoenix plug), connects all the devices together on an RS-485 network.

The "485 serial driver" that you see under the Runtime tab in FactoryTalk View Studio is a DH-485 protocol driver and would be the correct driver for these two DH-485 configured devices to communicate. There is no need for any other driver to be used where 1761-NET-AICs are used.

If they were successfully communicating, and nothing was changed, or was added, and they just stopped communicating, then...

The first thing I would physically check is the AICs...

Are the LEDs on all AICs active?

If not...

AICs would normally require external 24VDC power to their bottom terminals. Is there wiring on these for all the AICs and where there is wiring, do they have 24VDC power?

Note: Any AIC, who has a MicroLogix controller connected to its 8-pin Mini DIN port 2, does not require the external 24VDC power. The MicroLogix port 0 can power the AIC. So it is possible that the AIC at the MicroLogix in question does not have external power applied. However and optionally, external power can still be used.

If an AIC has external power connected then check the "DC Source" selector switch is set to "External".

If a MicroLogix is connected to an AIC on its 8-pin Mini DIN port 2, and no external power is connected, then make sure the "DC Source" selector switch is set to "Cable".

The baud rate for the DH-485 network may be fixed at something like 19.2kbaud, but I would usually recommend that all AICs have their baud rate switches left set to "Auto".

Each device on the DH-485 network should have a unique node address. Do you know all the node addresses?

Can you go online through your programming computer, using RSLinx Classic, to the DH-485 network and check which node addresses you can or cannot see?

If there are 5 active devices connected to the 5 AICs, then you should be able to see 5 nodes in RSLinx Classic? You may be able to see 4 nodes, for instance, which would indicate which node the problem is specifically with.

If none of the above yields anything, I would also check the physical network in case a network segment between AICs is down or damaged.

Just to be clear, what message does the PanelView Plus currently display?

Regards,
George
 
Hi Geospark,

Thanks for the very informative answer. The micrologix port you refer to I assume is the channel 0 tab within the Channel configuration menu?
 

Similar Topics

I lost the manual for this machine built in 2003 and need to put it back together. I have the Micrologix 1200 and PanelView 300 Micro programs...
Replies
4
Views
1,762
Hello Everyone, Please forgive me for some of my ignorance, I am relatively new to the PLC community. I am setting up a machine monitoring...
Replies
5
Views
2,152
I would like to know if it is possible to connect a Panelview 1000 (cat 2711-T10C8) that has DH+ to a micrologix 1200 with or without a AIC +...
Replies
1
Views
2,216
I do not use AB products much and need some help getting a few things to work using a Micrologix 1200 and a 4" Panelview 800. The software that I...
Replies
5
Views
7,785
Hey Guys, Work is a little slow and I have a project to control I would like to nut out hopefully... but these are the parts I have though I...
Replies
0
Views
2,556
Back
Top Bottom