Add another Ethernet Module

asterof

Member
Join Date
May 2007
Location
Califonia
Posts
554
BxFGUU5yOaI2Evq+gEPo6ijOJ8RHMk7GUVnTD6OADAc+BhrJOx74EHAFBnuKWewpOkAQDwsuDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2uDjAADa4OMAANrg4wAA2vwfD9yeA2H4E+0AAAAASUVORK5CYII=




1769-L33ER

with six modules and one power supply
It has one Ethernet port built in
Can I add another Ethernet card at the end of the chassis
See attached
and which card would it be
Thanks

chassis.jpg
 
No, they don't make Ethernet adapters for the 1769 series.

You could change your controller and power supply to something like the 1768-L43, then you'd have to buy 2 1768-ENBT's. They 1768 series use the same 1769 IO, but allow a few different types of communications adapters to be added to the left of the controller.
 
Why do you need two networks? Are you trying to isolate drives and other remote I/O from a plantwide network? If so, try using a 9300-ENA (or one of the new Stratix switches that have NAT capabilities) and setup NAT rules route between the two networks.
 

Similar Topics

Good afternoon: we have existing HMI created by FTV studio ME V8.0 which connects PLC1-roslogix5000, now we want to add one numeric display (its...
Replies
2
Views
1,698
So I have a Modbus device, it's register list states: Flow Rate: 400160 - Float I set up my MSG instruction, My Modbus node is 1, comms are...
Replies
23
Views
5,902
Hello everyone, I have a system using AIC+ to connect with Micrologix 1500 and Panelview 600. Now I want to add another panelview 600 HMI 15...
Replies
8
Views
3,832
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
Replies
1
Views
118
I have just installed Studio 5000 V30.11 on my Windows 11 Pro machine. First I had an "Invalid Pointer" error that required me to update Factory...
Replies
2
Views
117
Back
Top Bottom