DC motor torque % formula

bwiring

Member
Join Date
Nov 2005
Location
mpls. mn.
Posts
66
Can anyone help me with a formula for % torque of a dc motor. The application is a extrusion machine with a dc drive powering the motor. My customer needs to display the % torque of the output shaft of the motor/gearbox. Any help or suggestions would be appreciated.
 
Can anyone help me with a formula for % torque of a dc motor. The application is a extrusion machine with a dc drive powering the motor. My customer needs to display the % torque of the output shaft of the motor/gearbox. Any help or suggestions would be appreciated.

On the motor datasheet / nameplate, you should see a rated speed and current draw. I don't do much with large DC motors but with smaller units (< 1.5HP), at 100% of the rated current draw, the motor will output 100% of the rated torque.
 
It is assuming the field current is held constant at full nameplate current. Then shaft torque is directly proportional to Armature Amps with full load nameplate amps being 100% and Full Load torque being calculated from nameplate hp and nameplate base speed.
 
I am going to assume there is a DC drive running the motor. You should be able to set up an analog output to give you torque. You might even be able to directly access that parameter from the HMI via comms.
 
please see attached figure

This is what I talked about ,one of your DC drive analog analog outputs can be configured for torque display. This case is a poweflex DC dive, please check yours. That output can be connected to your PLC.
 

Similar Topics

We have aspindle that we drive with Siemens Sinamics S210 servodrive and servomotor1FK2104-4AF10-0MA0 and gearbox...
Replies
0
Views
1,624
Why it is said Maximum torque of induction motor is inversely proportional to frequency square ? Maximum torque formula for induction motor is...
Replies
13
Views
4,464
have a question. Hope i can ask it so it makes sense. Have a gear motor that is rated at 650 lb_in that turns 47 RPM at max speed. Need to use...
Replies
7
Views
2,106
I have an application where I am camming a rotary axis to a master axis driving a web material. The cam profile is fairly simple. The axis is a...
Replies
3
Views
1,769
trying to understand torque. thought it was the vfd. it was a two speed motor. torque seems to be more a product of the motor instead of the vfd...
Replies
5
Views
1,395
Back