What exactly is the situation?
1) Have these transmitters ever worked properly, or is this a new installation commissioning problem?
2) You obviously have multiple transmitters for each flow computer. Presumably, the PT, DP, and the TT are in close proximity to the flow element, so is the wiring to the flow computer approximately the same distance/length for the PT, DP and TT, for each flow computer?
3) Are the three problem transmitters on 3 different flow meters?
4) I can not make sense of the power supply drawing. I take it that your answer that the power supply is not common means that each of these problem transmitters has a different DC power supply, correct?
5) Are the R200 objects on the power supply drawing pt2 200 ohm resistors? I/S barriers? fuses? What are the R200 objects?
6) For any given flow meter, the TT and DP transmitters are powered from the same power supply as the PT with the HART problem, correct?
7) You have tested the HART communicator on the TT and DP xmtrs and these do not have a HART problem, correct?
8) Approximately what is the wiring distance between the xmtrs and the flow computer? 10m? 100m? 1000m?