Hi Guys,

I am looking for the difference in the two profinet specifications

What is the difference between Profinet 2.2 and 2.3?

I am asking this as a profinet device calls for it.

Thanks
 
Hi Guys,

I am looking for the difference in the two profinet specifications

What is the difference between Profinet 2.2 and 2.3?

I am asking this as a profinet device calls for it.

Thanks


I think the main difference was a hypothetical increase in bus speed (fastest update rate is now 31.5 microseconds via IRT). I'm not sure how many PN controllers actually support that bus speed (probably not many), but it's hypothetically available now.

If the device says that it SUPPORTS v2.3, it probably supports v2.2 as well. If the device REQUIRES v2.3, then that is a different story.
 
Thanks for the quick response. I will refer back to the documents now. It will support 2.2 just needed to know what advantages of 2.3

Thanks again!
 
There must be a difference in supporting bigger modul sizes.
I had two problems setting up a Profinet-IO communication with a S7-300 and a S7-400 which both support only V2.2, and a S7-1500 which supports V2.3 as fas as I know.
In one case I had an Anybus PN-PN coupler with a single module of 512 bytes which had not worked on Siemens side. After we split the module in many submodules of smaller size then it worked.
Next case was a S7-1500 as I-Device with a module size of 400 bytes if I remember corectly, which was not working in a S7-400 with Ethernet-CP as PN-controller. After I split it into smaller modules it worked.
 

Similar Topics

I want to establish a Profinet network in my production plant to connect multiple devices, including a PLC, HMI, and multiple Profinet-based...
Replies
19
Views
552
Hi, I have a customer with a S7300 from around 2013 which they link to approx 25 inverters, 3 DP to DP converters and 5 IM153 remote I/O units...
Replies
8
Views
287
Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
Replies
39
Views
2,054
Greetings! Facing a problem I've not seen before. GE CPE100 unit, LAN2 set up as ProfiNet. Multiple Turck TBEN-L4-16DIP modules, and a...
Replies
3
Views
191
Hello. I cannot change the SendClock settings for a PROFINET IO device. I need to slow down the CODESYS PROFINET IO controller. What am I doing...
Replies
0
Views
175
Back
Top Bottom