PowerFlex 70 Monitor DigIn Values Over Network?

jrsnydley

Member
Join Date
Dec 2014
Location
Minnesota
Posts
155
Hello everyone, I have a PowerFlex 70 that is controlled by a 1756-L73 controller via a 1756-DNB and 20-COMM-D module. DigIn 1 Sel (parameter 361) is set to "1 - Enable" The 24VDC comes from the drive, through a pull cord, and back up to terminal 1 on the drive. I would like to monitor the value of DigIn 1. I am wondering if there is a way to do this over the network or if I would have to wire it up separately to a 1756-IB16I.
 
This should be relatively easy.

On the PowerFlex 70, Parameter 216 is the raw values of the Digital Inputs.

You can add that to a DataLink, which will require a re-configuration of the I/O connection and re-mapping in the 1756-DNB scanlist.

Or, you can send Explicit Messages to the Parameter object in ladder logic.

This would be a "Parameter Read", which is Service 0x0E hex (Get Attribute Single), Class 0x0F hex(Parameter), Instance 216 decimal (Digital Inputs), Attribute 0x01 (Value). The MSG block will gray out everything but the Instance field when you select "Parameter Read" as the service.
 

Similar Topics

Is there a way to pull the heatsink temp from parameters to the PLC? I've had a couple critical drives fault recently for failed heatsink fans. We...
Replies
2
Views
2,084
Hello everyone, I'm new here. First of all I just want to say that you guys are very knowledgeable and reading your posts on here has saved my...
Replies
4
Views
152
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
207
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
Replies
0
Views
123
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
Replies
1
Views
93
Back
Top Bottom