Hi everyone
i have a delta VFD-M series with RS-485 protocol RJ-11 (Modbus communication) and cm1241 rs-485 siemens module (6ES7 241-1CH32-0XB0)
so i needed to transfer the DB9 connector to RJ-11 to establish the communication between the vfd and the plc
the picture shows how i managed do adapt the two connectors
please correct me if am wrong

kind regards

RS485 db9 to RJ-11.png
 
If DB9 pin 1 is truly signal ground, then yes, you have the correct connections.


I have seen other devices use pin 8 for A(-), pin 3 for B(+) and pin 5 for signal ground.


Be aware that some manufacturers define the A and B driver lines backwards so that A to A and B to B does not work.


If the driver lines are connected backwards, there's no damage, but communications will not work. The fix is to swap the lines on one end.
 

Similar Topics

Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
72
Hi all I need help on this As in my project used Schneider TM241 controller. Now I want to communicate Elite energy meter with controller by...
Replies
3
Views
148
Hello, I need to access the bits from the fire system control panel through RS-485. So, I used Read Var block to read from the panel...
Replies
0
Views
179
Hi, i cant establish communication between fatek plc with an energy meter, both capable for modbus tcp, i did with modscan but fatek plc does not...
Replies
1
Views
149
Hi Guys, I am a new member and this is my first post! I have a little PLC experience but it is mostly with siemens logo and using ladder...
Replies
4
Views
897
Back
Top Bottom