Micrologix 1200

LuisR

Member
Join Date
Jun 2020
Location
California
Posts
4
Hi to all,
we have a micrologix 1200 that changes mode by itself form run to program mode, don't know what may be causing that!, any idea?.

Can't change mode not even when cycling power, laptop is needed to change mode, then everything works fine for days,,,, then again.

Thanks in advance for any tips.
 
1) Is it also faulting?


2) If you cycle the power when it is in Run mode, does it go back into Run mode after the power comes back? If not, is it possible there is an infrequent power loss causing this issue (loose wire, etc.)?
 
Yes it does shows fault, faults goes off at powerup but goes to program mode.
Will double check that next time that happens, maintenance tech powered system down before I was able to connect.

Seems interesting to try the power conditioner
 
FYI, I did set the bit to run on powerup for the next time and definitely will try a power conditioner, the thing is that this machine has been working with no issues for 2 years and suddenly this situation came up.

Thanks all.
 
The fault probably means there is a problem in the program. I am guessing, but I suspect the 1400 "remembers" there was a fault and so "declines" to go into Run mode until the program is fixed. The next time this happens, connect to the 1400 with RSLogix and "Go Online," then "Goto Error."


Then the fun starts. Since this only happens every few days, perhaps there is an accumulating value that eventually overflows; look for +/- 32767 in Integer files, or +/-2G in Long files. Another likely issue is an indirect address that is out of range. However, these are all guesses; without having the program no one here can help much, and there is no guarantee that it is even a software issue. Was the program changed recently?
 
Last edited:

Similar Topics

Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
Replies
8
Views
587
I have a MicroLogix 1200 that has an 8 input and a 16 output. Every 6 months-year I get a fault and when online go to error it is something like...
Replies
3
Views
486
Have a bad output on a Micrologix 1200. Moved wire over to an available output, changed program to associate with new output. downloaded program...
Replies
8
Views
746
I need help achieving the following task: ML1200 sending 4 to 20 mA thru analog output ch0 to a DC speed controller analog input(4 to 20 mA) my...
Replies
3
Views
665
Hi there I am new with this thing and i don't know how to connect Allen Bradley Micrologix 1200 PLC to Raspberry Pi using USB to RS485 in NodeRED...
Replies
3
Views
2,257
Back
Top Bottom