WinCC Flexible and refreshing the values of variables

Iner

Member
Join Date
Mar 2010
Location
France
Posts
190
Hi,

I would like to know if there is a way to refresh the variables of only the current screen instead of refreshing all the variables ? The connection I use is a 9600/s and it can't take the more than one thousand variable I have.

I have seen there is a event associed with the buttons allowing to refresh a selected variable. But it would mean I would give a very long time of refresh to all other variables, and I would need to associate the variables of all a screen by one button, the button who will make the screen come. But after it would not refresh.... Is there a way to press a button automatically?

I don't like this solution so if an option allowed just to refresh the current screen, I would like to know it and it would help me a lot. Thanks in advance.
 
In WinCC Flex > Tags > Select tags in groups of 500 or less > General options > Acquisition Mode > Change to: Cyclic on use.

Now they'll be updating cyclicly only when they are used in the current active picture.
 
The normal is that the tags are to update "Cyclic on use", which means they will update only if they are displayed on a screen.
Some tags must be updated "cyclic continously", such as alarm tags.

Which PLC is this ?
 
Thanks for the answers.

Apparently yes, it was the option by default of the majority of the tags when made appear the option.

It is a TSX premium 57. I am using the Unitelway connection and I made a cable to connect the MP377 and the PLC.

My problem is that the connection works perfectly when I try to extchanges 15-20 tags.

But when I put all my application, I see in the alarm window that the connection is enabled, then interrupted, then enabled, then interrupted, and a part of the tags on the screen are refreshed, then disappear replaced by somes errors signs, then there are other tags who are refreshed etc... etc... And even on screens where there is nog a lot of tags.
 

Similar Topics

Hello everyone I Have an Issue with the usage of recipes in Wincc Flexible 2008, I create the recipe to change the values in a fast way The...
Replies
0
Views
69
Hi colleagues.We do data logging system.We want to record three temperatures under a certain condition. We prepared the project as follows. We do...
Replies
1
Views
736
Hello to everyone. I change the value of a "PQW" with a button in Wincc flexible. The code of the button is defined as M102.0. Value reset...
Replies
10
Views
4,524
Hello Friends I have installed WinCC Flexible 2008 SP5 Update 2. I have open the software, but the Transfer option does not appear. Is It...
Replies
2
Views
1,410
Hello everyone, is it possible to make a project that will not be used at the end of the specified date with wincc flexible?
Replies
5
Views
1,989
Back
Top Bottom