Weintek HMI tag addressing for siemens S7-300

sultanahmed

Member
Join Date
Jul 2013
Location
home
Posts
63
Hi,

How to define Siemens(S7-300 via MPI) plc tags in weintek HMI Mt8102?
I know Communication is established but i am not defining addresses correctly.

how to define addresses in HMI?
M33.3 ?
M100.4
DB3.DBW102?
I9.2
Q11.5
MD200
MW15

Experts advice required.
 
I’ve not actual used a 300 on a weintek but I think it’s
M33.3 = M-333
M100.4 = M-1004
DB3.DBW102 = DNn-3102
I9.2 = I-92
Q11.5 = Q-115
MD200 = MD-200
MW15 = MW-15
 