UPS for PLC (off topic)

What brand would you consider?

  • APC

    Votes: 7 70.0%
  • Tripp Lite

    Votes: 1 10.0%
  • OEM / Roll your own

    Votes: 2 20.0%
  • Perpetual Motion

    Votes: 0 0.0%

  • Total voters
    10

plc.doctor

Lifetime Supporting Member
Join Date
Aug 2002
Location
N36° 15.307' W119° 38.828
Posts
73
I'm looking for some ideas :unsure: for a UPS (uninteruptible power source) for a PLC. We have an AB PLC-5/40L with an external power supply (1771-P7) running some critical processes and need to prevent the PLC from rebooting during short losses to the supply power. I know this forum is for programming issues but I'm hoping that someone has run across this and I'm for some pointers in the right direction.
Thanks in Advance
 
I voted for APC because it's the only one I've heard of.
Although Perpetual Motion is great when you can get it.
:p
 
I've been in similar situations in the past.
However, I found that careful use of memory areas, and ensuring the battery backup was working correctly, allowed the PLC to recover from a power outage and resume operation without needing a UPS.
I don't know about AB PLCs, but if you find a way of doing it you could avoid installing another piece of equipment.

Regards,
Doug
 
Short Losses......

Doc,
Your solution lies in the exactness of your problem. What type of time period does "short losses" entail? Have you thought of also going with redundant PLC's (if the process is that critical) in case of problems with the main processor. There is a section of configuration in AB PLC's (DIP switches on the rack) where you can configure the I/O to remain in it's last state when hardware failure occurs. A UPS would also ensure that your process remains safe. I would opt for all of the above actions.
 
PLC UPS

I have used the following UPS: ONEAC #ON400XRA-SO

ONEAC used to make a UPS specifically for PLC's but for some reason
they have stopped making them. The above model does a good job,
it will hold up for at least 15 minutes.

For some projects it is necessary to have UPS and not
just a tracking filter or a good clean power supply.
 
UPS Specification

I prepare submittals based upon specifications prepared by the consulting engineering firm. Frequently a UPS will be in the spec. Sometimes they will give a minimum time that the system must run on battery. I do maximum load calculations and come up with a VA number. I like Powerware and Best. I have been using them for a few years.
http://www.bestpower.com
 

Similar Topics

I am using a Phoenix Contact UPS (QUINT USP) and I want to display information about the UPS state (battery charge percentage for example) in the...
Replies
6
Views
3,736
Looking for a UPS that integrates well into a L8xE Control logix installation. We have used the AB 1609-D1500N Ethernet IP UPS's in the past, but...
Replies
7
Views
1,899
I was asked to find a PLC backup for power outages. Does anyone have any recommendations of a system they have used and if so, how long will it...
Replies
24
Views
5,807
Dears, for indoor located PLC cabinet, my preference is to use UPS for supplying the PLC cabinet, PLC cabinet is located indoor and the UPS will...
Replies
1
Views