This is going to sound like a stupid question, but here goes. Here is the problem, last week a program change was made to SLC500 and the tech did not put the PLC back into run, just back to remote. The answer is simple to make sure you put in back in run, but is there a way to automatically do that or alarm if its not done? Just trying to make it bullet proof.
 
take a look at bits S:1/0 through S:1/4 - as shown below ...

you should be able to come up with a specific combination of ONES and ZEROS to determine what mode the processor is in - and the position of the keyswitch ...
.

slc_mode_bits.PNG
 
Last edited:
The alarm will have to be external from the PLC however, or tied to an output that isn't held on once the PLC is out of run perhaps.
 

Similar Topics

Hello. I have a connection between 2 CPUs over Network IO and I am exchanging data. but I want to stop the other CPU and continue. According to my...
Replies
2
Views
1,543
We are looking into installing a well water pump (480vac, 25hp, 40FLA) with a PowerFlex 755 VFD. The challenge is that the well is located about...
Replies
13
Views
4,554
I should know this by now but have never been given a straight answer...seems like they almost do the same thing. I am using Studio 5000 by the way.
Replies
7
Views
4,069
I have a Control Logix PLC and Safety PLC , 5581ES and 55L8SP respectively, pulled out of a cabninet connected to a Panelview Plus connected over...
Replies
2
Views
1,545
Good Morning , I need to make a online change to a SLC 500 5/05 . Is it safe to turn the key from Run to Remote with causing the processor...
Replies
2
Views
1,852
Back
Top Bottom