Siemens CPU313C Analog Inputs

sherman4

Member
Join Date
Jun 2002
Posts
46
Hi !

I am new to Siemens S7300 (313C CPU) PLC and I cannot find the documentation related to analog inputs connecting diagrams.

I have a couple of active flow transmitters (4-20 mA) 120Vac powered, which I would like to connect to the PLC AIs, I have connected passive transmitters before to the same inputs (following the diagram on the module cap), but I am afraid that it might not be the same connection type for active 4-20mA transmitters (no 24 Vdc powers the 4-20mA loop).

If anyone does have connecting diagrams available or any web link, please help. I appreciate it.

Thans
 
[attachment]
In the above example (for channel 2) you would have to connect the 4-20mA signal on pin 9.
If you use channel 0, you will have to connect the 4-20mA signal on pin 3.
Connect ground to pins 4-7-10-13-20. The ground must be looped back to the device that generates the 4-20 mA signal.

313c_analog.gif
 

Similar Topics

Hallo everybody Im pretty new in here about 2 min he he, i would like to get som help setting up my PLC, i have worked with step 7 before but...
Replies
1
Views
3,263
Hi everyone, i have a Siemens S7-300 Cpu 314C-2 DP with several cards of i/o and servos my laptop has TIA version 16 and 17 loaded and...
Replies
3
Views
4
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
2
Views
19
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
26
Views
308
Hi everyone, I am an omron plc tec , lately I came across a siemens s7 200 cn plc . Can someone help me regarding the software required and...
Replies
26
Views
471
Back
Top Bottom