Jean-Philippe February 2nd, 2010 02:31 PM

Panelview 900 problem Error 60
 
Hi everybody, I'm new in this forum. I have a Panelview 900 without user manual. The problem: The screen starts to flick, and "Error 60" was displayed on the screen. The touchscreen was unresponsive. I cycled the power and they never restart. The red light (fault) always stays on and even when I push "RESET" on the back nothing happen. Can you help me?

Jean-Philippe February 2nd, 2010 04:18 PM

And do you think when you press "RESET" on the back, you lose your program?

barryoc February 2nd, 2010 04:44 PM

Jean,
Manual available here. See page 236

http://support.elmark.com.pl/rockwel...M014A-EN-P.PDF

jrwb4gbm February 2nd, 2010 05:02 PM

Quote:

Originally Posted by Jean-Philippe (Post 358448)
Hi everybody, I'm new in this forum. I have a Panelview 900 without user manual. The problem: The screen starts to flick, and "Error 60" was displayed on the screen. The touchscreen was unresponsive. I cycled the power and they never restart. The red light (fault) always stays on and even when I push "RESET" on the back nothing happen. Can you help me?

Pages B-17 and B-18 in the manual shown in the link above have the answers to your questions.

Jean-Philippe February 2nd, 2010 06:07 PM

Thank you guys for the hints. So "error 60" is "CPU could not execute code". Do you think that the system is corrupted? When I try to reboot-it, instead of the "Self-test startup page", I only see unreadable characters and the screen turn black.

Ken Roach February 2nd, 2010 06:46 PM

All those symptoms are consistent with a failed terminal. "Failed", as in broken and probably unfixable.

And that's bad news. The application program cannot be retrieved if the operating system can't boot.

The PanelView 900 Standard hasn't been manufactured for 5 years or so. The PanelView 1000 Standard terminals are still being built brand new.

For most failed PanelView 900 terminals, I try to do a conversion to the newer PanelView Plus platform.

Jean-Philippe February 2nd, 2010 07:47 PM

Quote:

Originally Posted by Ken Roach (Post 358497)
All those symptoms are consistent with a failed terminal. "Failed", as in broken and probably unfixable.

And that's bad news. The application program cannot be retrieved if the operating system can't boot.

The PanelView 900 Standard hasn't been manufactured for 5 years or so. The PanelView 1000 Standard terminals are still being built brand new.

For most failed PanelView 900 terminals, I try to do a conversion to the newer PanelView Plus platform.

Thank you for your time. I will remove the Panelview of my system: I will install an Honeywell Experion Station with a graphic display to replace it. This system was from a closed plant in Texas. We bring back some equipments in Canada and we tried to use it here but... That's ok. :thumb: