Please I have micrologix 1500&1200
The first time I make configuration for 1200 it was ok and i see the plc but there was on it a old programme so I make clear memory to delete it and to download a new one but after that I can't see the plc again to download a new one.
On 1500 from the first configuration I can't see the plc.
Please can anybody help me to solve the problem ?
Thank you.
 
"I can't see the plc" by this do you mean you lost communication? If so you probably changed the comm port setting when you downloaded the new program. Take a look at the offline file to check the comm ports configuration.

You can use the "DCOMM" button to change channel 0 to it default setting temporarily to get connected. See below.. It works for both the ML1500 and your ML1200

The usual way to connect to a MicroLogix 1500 with an unknown protocol is to use the Channel 0 serial port and press the DCOMM button until the DCOMM LED comes on indicating that the controller has been temporarily switched to DF1 Full Duplex 19200 baud on the Channel 0 (built-in, round, min-DIN8) port.
 
I try it I still have the same problem . I mean I can't see the plc that only I can see the interface only or the USB port and down this one you must to see plc that you have it so I can't see it .
Thank you
 

Similar Topics

We had a DH-485 network with a SLC 5/02, PV 550, 2 Micrologix 1200, and Mircologix 1500. I need to know how to change the nodes of the 2 1200s...
Replies
4
Views
2,813
Hey everyone, I've got what I think is just a quick question here. I'm sending some data from one micrologix to another, there are already some...
Replies
0
Views
4,847
HI EVERYONE please read if I understood correctly : I have a rung consist of one input and one output(OSR instruction), when input on and then...
Replies
5
Views
6,445
What is the difference between the 1200 and 1500
Replies
7
Views
4,527
Good Day i Have Micrologix 1500 LSP, and I want to get data from plc and send it through Modbus RTU slave; I have only ch0 on that plc I Order...
Replies
6
Views
868
Back
Top Bottom