Confused 1756 ENBT
wa5yom
Sep 2003
Ardmore, Oklahoma
138
I have 6 machines all configured and programmed the same....only difference is the IP....
In the RsLinx Driver Diagnostics it shows to be a CSPv4 connection instead of a Ethernet/IP connection...
Any thoughts?
Tim
The 1756-ENBT doesn't support the CSPv4 protocol, at all. So either the target device isn't a ControlLogix, or the indication in RSLinx Classic is incorrect.
Exactly where are you seeing this in RSLinx Classic ?
Are there other functional problems other than this indication ?
It is not indicated properly and the Driver Diagnostics shows a CSPv4 connection...and I cannot go on line........but the communications (msg) is working correctly....my initial though was that some other device was online with that IP....but I disconnected the machine from the network. pinged it. and nothing else showed up....
Connection Log' the The IP group is 10-24-9-249 through 254 and the node in question is 251
05/13/13 08:36:39 10.24.9.249 Attempting first connection, protocol = CSPv4
05/13/13 08:36:40 10.24.9.250 Attempting first connection, protocol = CSPv4
05/13/13 08:36:40 10.24.9.251 Attempting first connection, protocol = CSPv4
05/13/13 08:36:40 10.24.9.252 Attempting first connection, protocol = CSPv4
05/13/13 08:36:40 10.24.9.253 Attempting first connection, protocol = CSPv4
05/13/13 08:36:40 10.24.9.254 Attempting first connection, protocol = CSPv4
05/13/13 08:37:01 10.24.9.251 Device has accepted the CSPv4 connection
05/13/13 08:37:01 10.24.9.251 Can't set port type to 28: no Harmony object for this Ethernet
05/13/13 08:37:02 10.24.9.254 Unable to establish TCP connection to the Ethernet Interface
05/13/13 08:37:02 10.24.9.254 [10061] Connection refused
05/13/13 08:37:02 10.24.9.254 Device refused a CSPv4 connection, retry using EtherNet/IP
05/13/13 08:37:02 10.24.9.254 Attempting first connection, protocol = EtherNet/IP
05/13/13 08:37:02 10.24.9.249 Unable to establish TCP connection to the Ethernet Interface
05/13/13 08:37:02 10.24.9.249 [10061] Connection refused
05/13/13 08:37:02 10.24.9.249 Device refused a CSPv4 connection, retry using EtherNet/IP
05/13/13 08:37:02 10.24.9.249 Attempting first connection, protocol = EtherNet/IP
05/13/13 08:37:02 10.24.9.252 Unable to establish TCP connection to the Ethernet Interface
05/13/13 08:37:02 10.24.9.252 [10061] Connection refused
05/13/13 08:37:02 10.24.9.252 Device refused a CSPv4 connection, retry using EtherNet/IP
05/13/13 08:37:02 10.24.9.252 Attempting first connection, protocol = EtherNet/IP
05/13/13 08:37:02 10.24.9.250 Unable to establish TCP connection to the Ethernet Interface
05/13/13 08:37:02 10.24.9.250 [10061] Connection refused
05/13/13 08:37:02 10.24.9.250 Device refused a CSPv4 connection, retry using EtherNet/IP
05/13/13 08:37:02 10.24.9.250 Attempting first connection, protocol = EtherNet/IP
05/13/13 08:37:02 10.24.9.253 Unable to establish TCP connection to the Ethernet Interface
05/13/13 08:37:02 10.24.9.253 [10061] Connection refused
05/13/13 08:37:02 10.24.9.253 Device refused a CSPv4 connection, retry using EtherNet/IP
05/13/13 08:37:02 10.24.9.253 Attempting first connection, protocol = EtherNet/IP
05/13/13 08:37:22 10.24.9.254 Device has accepted the EtherNet/IP connection
05/13/13 08:37:22 10.24.9.254 Can't set port type to 288: no Harmony object for this Ethernet
05/13/13 08:37:22 10.24.9.252 Device has accepted the EtherNet/IP connection
05/13/13 08:37:22 10.24.9.252 Can't set port type to 288: no Harmony object for this Ethernet
05/13/13 08:37:22 10.24.9.250 Device has accepted the EtherNet/IP connection
05/13/13 08:37:22 10.24.9.250 Can't set port type to 288: no Harmony object for this Ethernet
05/13/13 08:37:22 10.24.9.249 Device has accepted the EtherNet/IP connection
05/13/13 08:37:22 10.24.9.249 Can't set port type to 288: no Harmony object for this Ethernet
05/13/13 08:37:22 10.24.9.253 Device has accepted the EtherNet/IP connection
05/13/13 08:37:22 10.24.9.253 Can't set port type to 288: no Harmony object for this Ethernet
Okay, so the essential problem is that you can't go online with that controller.
Are you using the RSLinx Classic 'Ethernet Devices' driver, or the 'EtherNet/IP
driver ?
Can the RSWho browse see the 1756-ENBT ?
Can you bring up the diagnostic web page of the 1756-ENBT ?
It's possible that the driver configuration got confused during establishment of the device type, and thinks that your Logix controller is really an SLC or PLC-5. I've never seen that happen, but that's the stage at which the Ethernet Devices driver determines whether to use CSPv4 or EIP.
Try creating a new driver, either 'Ethernet Devices' or 'EtherNet/IP', and let it browse.
Okay, which one am I supposed to be looking at ?
With those Harmony object errors, I would go ahead and delete the Harmony.HRC and Harmony.RSH files in the /RSCommon director and reboot.
I have re-created the Ethernet Driver a few times.....with no change in the results......I am using the Ethernet Device Driver
The device in Question is the 10.24.9.251...
Does your computer also have that address ?
A 1756-ENBT cannot accept a CSPv4 connection: they don't support that protocol, which uses TCP Port 2222.
But we see 10.24.9.251 accepting the CSPv4 connection, and also identifying itself as a Computer (really, an RSLinx station).
Try PINGing 10.24.9.251, then doing an 'arp -A' from the command line to see if you can determine the MAC ID of the device.
All 1756-ENBTs will have a MAC ID beginning with 00-00-bc.
Change IP address in RSlinx driver to 10.24.9.251:EIP
This will force to conenct with CIp a bypassing initail CSP connection
Contr_Conn is of course correct, but I'm not sure what making that change will do.
Something's wrong if that IP address is accepting a CSPv4 connection. It should refuse a TCP connection directed to Port 2222.
I suspect very strongly that there is a computer on this network with the same IP address as the controller.
It might be time to roll out the big guns: Wireshark.
That actually suggests *more* that it's a computer.
A 1756-ENBT always replies to a PING, but some computer operating systems block PING. Any chance somebody is running a VMWare instance of XP with that IP address ?
There's a great command-line utility called 'TCPing'.
http://www.elifulkerson.com/projects/tcping.php
Try doing a TCPing with Port 2222 and see what device answers.
Microsoft Windows XP [Version 5.1.2600]
(C) Copyright 1985-2001 Microsoft Corp.
C:\>tcping 10.24.9.251 port 2222
1 extra argument ignored. FYI.
Probing 10.24.9.251:0/tcp - Socket is not connected (10057) - time=2002.232ms
Probing 10.24.9.251:0/tcp - Socket is not connected (10057) - time=2001.668ms
Probing 10.24.9.251:0/tcp - Socket is not connected (10057) - time=2000.102ms
Probing 10.24.9.251:0/tcp - Socket is not connected (10057) - time=2000.039ms
Ping statistics for 10.24.9.251:0
4 probes sent.
0 successful, 4 failed.
Was unable to connect, cannot provide trip statistics.
Which of the following input operations require a conversion to digital form prior to input? a) disk b) analog c) contact closures d) limit...
3,825
Hey all! I recently purchased myself a Panelview Plus off of ebay and i was hoping that i could upgrade the firmware on it to Version 9 or so and...
2,692
Good morning everyone. I am apparently confused on the COP instruction. What I am trying to do is copy a DINT to a DINT in a User Defined Data...
16
6,786
Hey guys, Im currently using the above flex IO to turn on two outputs these outputs go to two flashing red beacon lights. Here's the scenario: My...
1,681
I'm event AV Technician (Sound, Projection, and Lighting). Over the last couple of years I've used a Weigl ProCommander PHX to control some event...
2,670
