HI All,

I have to use thermocouple (sine the give voltage as output), and I have two analog inputs in my TM221CE16R, which are voltage dependent (0-10v, with LSB of 10mV). How can I do that? I guess I cant do this directly, does anyone know of any reliable, but a bit cheap amplifiers for Thermocouples? The other option is to but the extra cartridge for thermocouples by Schneider Electric.

Any suggestion?

Thanks.
 
Look at how little voltage a thermocouple produces (approximate values):

Type K 0 to 1200 Deg C = 0 to 48.8mV, 1 Deg C change ranges from approx 0.039mV to 0.034mV
Type J 0 to 1200 Deg C = 0 to 69.5mV, 1 Deg C change ranges from approx 0.050mV to 0.057mV
Type T 0 to 400 Deg C = 0 to 20.8mV, 1 Deg C change ranges from approx 0.039mV to 0.062mV

A 0 to 10Vdc input does not have enough resolution to handle is too such small changes as 0.034mV (0.000034V)/deg. That's 10.0V/0.000034 = 294,117 parts of resolution = 100 0111 1100 1110 0110 which would require a 19 bit A/D converter to resolve a 1 degree C change in K type thermocouple, assuming no noise

The suggested alternative is to use a temperature transmitter which produces a 0-10Vdc output proportional to a scaled temperature input.

Be alert to the fact that a configuration tool for scaling the temperature (0-100 Deg? 200-400 Deg C? 0-1500 Deg C?) over the range of the output (0-10V) requires some means - keyboard and display, PC with Modem and software, HART communicator, all of which cost something.

If you're not will to spend money on a configuration tool, look for a vendor that sells a transmitter pre-configured to the range you need, or who will configure it for you for some nominal fee.

Also be aware that a grounded thermocouple with a non-isolated transmitter can create a ground loop the looks like a tempeature offset.

My suggestion is to always buy 'ungrounded' thermocouple assembly.
 
Look at how little voltage a thermocouple produces (approximate values):

Type K 0 to 1200 Deg C = 0 to 48.8mV, 1 Deg C change ranges from approx 0.039mV to 0.034mV
Type J 0 to 1200 Deg C = 0 to 69.5mV, 1 Deg C change ranges from approx 0.050mV to 0.057mV
Type T 0 to 400 Deg C = 0 to 20.8mV, 1 Deg C change ranges from approx 0.039mV to 0.062mV

A 0 to 10Vdc input does not have enough resolution to handle is too such small changes as 0.034mV (0.000034V)/deg. That's 10.0V/0.000034 = 294,117 parts of resolution = 100 0111 1100 1110 0110 which would require a 19 bit A/D converter to resolve a 1 degree C change in K type thermocouple, assuming no noise

The suggested alternative is to use a temperature transmitter which produces a 0-10Vdc output proportional to a scaled temperature input.

Be alert to the fact that a configuration tool for scaling the temperature (0-100 Deg? 200-400 Deg C? 0-1500 Deg C?) over the range of the output (0-10V) requires some means - keyboard and display, PC with Modem and software, HART communicator, all of which cost something.

If you're not will to spend money on a configuration tool, look for a vendor that sells a transmitter pre-configured to the range you need, or who will configure it for you for some nominal fee.

Also be aware that a grounded thermocouple with a non-isolated transmitter can create a ground loop the looks like a tempeature offset.

My suggestion is to always buy 'ungrounded' thermocouple assembly.

you are righ on spot..I feel that using an RTD or thermocouple with the temperature input module(which I have to but extra) of my PLC will be the best option.
 

Similar Topics

Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
38
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
72
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
Replies
4
Views
82
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
158
I am trying to set up a piece of equipment with a Horner HE-X4R. I'd like to use structured text and so far I'm just trying to get a basic On/off...
Replies
0
Views
66
Back
Top Bottom