SRTP is GE's serial SNP protocol adapted for Ethernet TCP/IP. The 90-70 only ever supported SNP through the serial port on the CPU module and SRTP through the Ethernet module.
To use Modbus RTU you would need a communications coprocessor module IC697CMM711.
Or else check your documentation of the Siemens HMI to see if it supports communication with GE PLCs using SNP or SRTP.