My first question would be what HMI software are you using FactoryTalk SE would make this pretty simple. Well... As easy as FactoryTalk makes anything else. But I agree with cjd1965. An HMI in a central location for monitoring, and as many as need to handle the local changes at the vats would be my first choice. Each HMI would be used to display information from, or give information to the PLC. All of the control programming should be handled in the PLC.

A type J thermocouple should work fine. If you want to bring the signal back as 4-20 you could use an RTD with a converter built into the unit. There may well be such a device for the thermocouple as well, but I'm not aware of one.