Hi guys,

I'm currently some problems with the RSNetWorx for DeviceNet application on my machine. The problem is that when I try to upload parameters from any connected node,Iget and error. I can go online and see the nodes but cant upload. I've tried ver 6.00 and ver 7.00 but its still the same. Any advice from the experts would be appreciated.

cheers,

RSNetWorx for DeviceNet.jpg
 
It is very likely a conflict between versions of RSNetworx and RSLinx Classic. RSNetworx is especially sensitive to mis-matches of the Coordinated Product Release (CPR) level.

I strongly recommend RSNetworx v10 and RSLinx Classic 2.55 or higher.
You may also use RSNetworx v9 and RSLinx Classic 2.54.

I have seen this issue with RSNetworx for DeviceNet version 9 and RSLinx Classic 2.54.
 
I always wondered what that CPR number was for.

Ken is there a matrix for CPR? I assume this is a number to designate which products work together.
 

Similar Topics

The back story: We have one customer that has some equipment that uses DeviceNet that must remain in place. On those (5) DeviceNet networks they...
Replies
2
Views
860
I have a PLC5 with an Ethernet card. It also has a devicenet network under it. Can I somehow use RSNetworx with it, over Ethernet? I have the...
Replies
2
Views
2,017
Good evening, I have a problem with the size of a WAGO module in devicenet. The configuration is as follows: DEVICENET BUS 750-306 750-430 8...
Replies
3
Views
1,899
Hello fellow programmers, I am looking for a DeviceNet file with at least 1 VFD (powerflex70 and 700 if possible) and 1 E3 for parameter review...
Replies
3
Views
1,382
Hi all Yesterday we had a failure with a powerflex 70 drive and had swap it with a similar replacement. The powerflex drive had a 20-comm-d...
Replies
2
Views
2,920
Back
Top Bottom