Does anyone have expierence with PIDE control of an on/off output.
I am converting a heat treat oven from temperature controllers to PLC based PIDE logic. This is a gas fired hardening furnace, not electric heaters with SS relays.
How do I convert the analog CV value to an On/Off. I don't really want to cycle my burners more that once per minute. When I get close to set-point I could cycle them On = x sec and Off = x sec over a one minute time but not sure how to go about it.
o_O
Any input would be greatly appreciated.

PS - All of my furnace safeties with this change are compliant, just need help with the control. I am doing heating only not heating/cooling.
 
If by PIDE you mean the Rs5000 Function block then see below.

Look at the SRTP function block, can set it up to not use the cooling output.
 

Similar Topics

There is a chilled water cooling loop in our process cooling a roller. It has been about impossible to tune. this is in a tertiary loop. From the...
Replies
6
Views
3,214
We have an oven with 32 zones and a Controllogix L7 controls the oven and all the steam valves, plate heaters and T/C's come in over different...
Replies
13
Views
5,436
I have created a PIDE loop in control logix and am for some reason unable to get this loop to function in AUTO. the outputs that are set telling...
Replies
1
Views
2,624
I am using the PIDE function in version 16 of RsLogix 5000 for a job which I am in the process of testing. The problem I am seeing is with the...
Replies
7
Views
6,013
Can anyone tell me the difference between program,operator and override modes with the PIDE instruction in RS Logix 5000, and when they are likely...
Replies
5
Views
4,171
Back
Top Bottom