Good Afternoon ,
We had to replace a Powerflex 70 2 HP with a 3 HP. These drives are on Devicenet . Once installed and transferring with the HIM , I was able to get rid of the flashing yellow on the STS LED . The 1747- Devicenet Scanner Module is reading 63 saying it is good.
When I turn the breaker off for the Powerflex 70 , the Scanner Module recognizes that it cannot communicate with that drive , and goes to , I think , a 73 or 78 . When powered up , everything looks fine , till I try to run it . It does
absolutely nothing . I look at it in the SLC 500 program , and I see no communication with it .
I open up RS Networx for Devicenet , I'm lost with that , When I try to go online with it , and browse , I get all these returns " Not Found at Address ## " .
A few questions....
- If Devicenet is seeing that drive , why wouldn't it be sending and receiving
information ?
- What would be the cause of not seeing the nodes on a Devicenet network ?
- Have you folks ran into this before ?
Thanks so much for your help .
We had to replace a Powerflex 70 2 HP with a 3 HP. These drives are on Devicenet . Once installed and transferring with the HIM , I was able to get rid of the flashing yellow on the STS LED . The 1747- Devicenet Scanner Module is reading 63 saying it is good.
When I turn the breaker off for the Powerflex 70 , the Scanner Module recognizes that it cannot communicate with that drive , and goes to , I think , a 73 or 78 . When powered up , everything looks fine , till I try to run it . It does
absolutely nothing . I look at it in the SLC 500 program , and I see no communication with it .
I open up RS Networx for Devicenet , I'm lost with that , When I try to go online with it , and browse , I get all these returns " Not Found at Address ## " .
A few questions....
- If Devicenet is seeing that drive , why wouldn't it be sending and receiving
information ?
- What would be the cause of not seeing the nodes on a Devicenet network ?
- Have you folks ran into this before ?
Thanks so much for your help .