Pulse Input Wiring
coopdegrace
Mar 2009
perth
34
Hi Guys,
I have a question regarding the wiring pulse output from a E&H flow meter.
Flow meter is a E&H 10P and input card is AB 1734-IB8
Question is how do I connect this up correctly so that I can read the pulse?
Do I wire the Pulse -ve (Terminal 25) to 0VDC and the Pulse +ve (Terminal 24) to my input?
Or Do I need do I need to supply 24VDC to the Pulse +ve (Terminal 24) and wire the Pulse -ve (Terminal 25) to my Input? If I do this will i need a current limiting resistor??
I have had some good help on this forum and just want to say its appreciated.
Cheers
This is a passive open collector output so you will need to provide the power for the pulse. You would do exactly what you what you said. 24VDC to #24 and #25 to your PLC input. Make sure you connect the COM of the input card to the same negative of the power supply you used for the pulse.
As for the Pull Up Resistor I would look at the manual for the meter to make sure. The E+H meters I have worked with in the past had an internal resistor so an external one was not needed. But check it out in the manual first.
One last thing to keep in mind is to make sure you set your K-Factor (pulses/volume) to a rate that the IB8 can handle. Also don't set your pulse width too small or the card may not count the pulse either. I have a spreadsheet that will compute your pulse width based on flow Fate and K-Factor. If you want it send me a PM and I will email it to you.
I just looked at the specs for the 1734-IB8 and you will not need a Pull Up resistor. It has a max draw of 5mA which is well under the 250mA max draw of the output.
PM me your Email address and I will send you that Spreadsheet.
Hello, We have the following DI card that can accept 1,2 and 3 wire DI's ( 6DL1131-6BH00-0PH1). We plan on installing this card for use with a...
1,475
Just finished an upgrade from a SLC500 to CLX where they had a 1746-HSCE and we're now using a 1756-HSC. Two wire pulse signal from the...
1,296
Hello all, I am working with a variety of discrete pulse flow meters, Siemens, Flomec, and Seametrics. I am attempting to read flow via discrete...
17
4,664
I want to read the pulse output from an ABB mag flow meter with a Modicon BMXDDI1602 discrete input module (positive 24VDC sinking). I will only...
2,428
Anyone know of a good TOF relay I can use to catch a high speed 24vdc (~100ms) and signal a 120vac input module? This is a pig that goes through...
2,780