OMRON CQ1 and NT600S

Alex Pel

Member
Join Date
Feb 2004
Location
Vancouver
Posts
145
Hello All.

I have no experience with Omron PLC and I am asked to find the problem in the working system. I have:

PLC – SYSMAC CQ1 CPU45-V1;

Soft - CX-PROGRAMMER 3.0;

HMI – NT600S (connected to PLC by the RS-232C method)

Soft – NT Support (can’t remember exact ver.)

I have uploaded the PLC program to CX-PROGRAMMER.

My problem is: - I couldn’t get on-line to NT600S.

Is it possible communication: PC (NT Support) -> CQ1 CPU45 - > NT600S?

Also I tried: PC (NT Support) -> NT600S? Unsuccessfully, may be wrong cable. Tomorrow I will try existing cable that connects CQ1 CPU45 - > NT600S.

I will be highly appreciated for any consideration
 
I think you can set the comms path to go though the processor, has been a while since I have done it, but from memory the function is there.

Just had a quick look, doesn't look like you can go through the NT support tool, you can with NS-Designer, or the new CX_designer.

The cable should be the same as the one you used to upload the PLC file.
With the NT screens however, you have to enable connection. I cannot find the manual on this procedure, but you press 2 corners of the NT screen, and then follow the menu system to enable transfer.

Hope this helps
 
Use this cable to connect PC (NT Support Tool) to NT600S.

PCtoNTcable.JPG
 
Last edited:
Thanks a lot. I was away from my computer over weekend. “Pressing 2 corners” it is the news for me, think it will help. I have already made the cable; wiring taken from OMRON web site. It is the same as IO_Rack said except last two missing conductors. I’ll try tomorrow.
 
Thanks everybody. It works. I pressed two corners and went to transfer mode. After that successfully uploaded the HMI NT600S.
 

Similar Topics

Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
1
I am working on a project using a NB screen and NX1P2 PLC. I am having a really hard time getting a real number to properly translate through to...
Replies
3
Views
102
Hi, I am facing an error inside Omron Network Configurator. I have 2 PLC communicate each other using ethernet cable, send signal using Network...
Replies
2
Views
88
I have a strange Kepware issue I have been dealing with for a few weeks. I have Kepware setup with the Omron NJ Ethernet driver and reading in...
Replies
0
Views
80
hi dear all hope you all are fine I have a problem with my CJ1M cpu11 ETN. it stop communication with PC over ethernet. ETN unit all indications...
Replies
4
Views
139
Back
Top Bottom