Check to make sure the "Settings" for the Host Link port are correct.

Next make sure the RXD instruction is set up correctly. The bottom value in the instruction is the number of bytes to receive. If this is not set properly, it can cause problems.
Also, make sure the data has been received on the port before you initiate the RXD instruction. There are "flag" bits that can be used for this purpose.

The progamming manual for the CPM2A is W353. You can download the manual from www.omron.ca. In the left menu click on Document Library. Enter W353 in the partial document number box and click search (or go?).

Good Luck. Let us know if you have any other questions.