Dear all
Iam using three load cells connected in parallel to calibrate the weight of a product but in don't have a weighting module in my system., I just used the analog input on my cpu 1215C (s7-1200) . But I have a problem in scaling the analog input and display ithe weight on the HMI
 
You cannot use a regular 0-10V or 4-20mA input with a loadcell or parallel connected loadcells.
The change in resistance is very small. The weak signal is measured in a socalled "wheatston bridge" configuration (https://en.wikipedia.org/wiki/Wheatstone_bridge).

When applied with an excitation voltage (typically 10V or in that magnitiude), it returns a signal in the mV range (typically 1mV/V, 2mV/V or 4mV/V). The wheatstone bridge helps with compensating for differences in the wiring to/from the loadcell.
You usually have between 4 an 6 leads from each loadcell, so I wonder how you have managed to connect it to a regular analog PLC input.
 
JesperMP is right,
if you are using 3 load cells to weigh something, you must use a summation system controller that is compatible or configurable with the load cells, program the unit, and then take its output and goto the plc.

we have over 50 of such systems here with load cells ranging from, 10k to 250k

james
 
I have wired three load cells in parallel and by using load cell ampilifier with 0-10v output , I scaled the analog input from 0 to 150kg . Now it works quite well
 

Similar Topics

I have a beam with a load cell on each side (under each end) If the maximum weight being pulled down on the beam is 1000lbs Do you buy two...
Replies
11
Views
2,683
Hello all, i will start off by saying i know nothing about load cells, i want a converter/amplifier to output a 4/20mA signal from a load cell...
Replies
14
Views
5,352
Hi all, Has anybody tried to read load cells using the Re Lion Graphite and any of the strain gage modules (GMSG1)? I was wondering if I can give...
Replies
1
Views
1,742
Hello Can I connect s7-200 (cpu 226) with load cells (SB 210) and indicator (SI510) using profibus EM ? What is the best and simplest way to...
Replies
2
Views
1,752
Hey guys. I'm looking for an inexpensive way to integrate 4 load cells into a project. Right now, the project is using an Arduino with a HX711...
Replies
13
Views
7,116
Back
Top Bottom