When you use Flash you can use Bootp and assign the address to the PLC then flash it

Or you can just get a crossover cable or null modem cable for the RS232

Here is a video I did awhile back that may help...

Allen Bradley 1769-L32e setting up Ethernet and flashing CPU http://youtu.be/FkO2BBuuwJw

Make sure you dont have both CPU's on the network with the same address