No, you can open ControlFlash... try to update a L32e with your address you want to flash, after a min it will error out and you can enter in the mac ID, by doing this it will use Bootp and will assign a IP address to the PLC, then you can flash it with using Ethernet IP

You do not need a serial cable but surprised if you dont have one laying around?