Panelview Plus 7 rare text behavior

MOL13

Member
Join Date
Dec 2019
Location
Bs. As.
Posts
5
Hi all, i was serching unsuccessfully something relationed with this issue.

I have a screen with several labels, some of them with the same "Y" position.
At TEST time in FTV all of them are displayed correctly but in Runtime on real machine they are displayed overlapping laterally, i mean las character from one mixed with first char of next one.
Resolution is the suggested in project properties for this panel, 640 x 480.

Any idea? Thanks in advance.
 
On your development PC, examine the text objects to see what font they use.

PV+ terminals by default have only the "Arial" font installed. On FTView ME version 11 and later, it's "Arial Unicode MS".

To support other fonts, you need to download a TrueType (TTF) font file to the PV+ terminal using the Upload / Download utility.
 
Ken, thank you for answering.
I´m working with FTV ME 9 version and I have several fonts to choose at design time, but only use Arial, in sizes 10 and 12.
I´m trying to understand if you say that I should download fonts packets TTF to panel device.
I would have liked to upload images from my disc but I only be able to URL link. Sorry, I am rookie on this Forum.

PS: I don´t find an "Upload / Download utility" on my entire FTV Suite.
 
Last edited:
Font upload is on the Terminal itself. I guess you have to put your font in a USB stick and attach it to the terminal and choose the source as external to copy when prompted
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
25
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
46
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
72
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
Replies
0
Views
87
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
125
Back
Top Bottom