I have the Omron CJ1M CPU and SCU31-V1 module for Modbus with Protocol Macro using PMCR instruction in the ladder. Here PLC is the master and Remote I/O cards are slaves. We have 13 Remote cards/slaves.

Is any other method for Modbus PMCR polling other than using a counter?
Time b/n polls or pollrate on a slave in 13 slave network is 1.5sec. I want to reduce this time.
 
Last edited:
I use a counter for this always.
There are 3 things that slow down polling - number of devices - size of poll and comms speed. Increase the speed and decrease the time - decrease the number of polls and decrease the time - decrease the size of the poll and decrease the time.
I normally poll a maximum of 4-5 devices at a minimum speed of 19,200 baud. I find it is quicker to do 2 polls to a device sometimes. If I want 3 words from one area and 3 words from another area it is usually quicker to do 2 polls for the 3 words each time than poll 50 words top get the same information in one block with a lot of other rubbish.
The SCU31 has 2 x RS485 - break the network into 2 and use both ports.
 

Similar Topics

Hi There. I have PC to get few tags from PLC into C# windows forms application. What is the best and fastest way? I could not find Omron in...
Replies
3
Views
161
Hello Guys, I have been trying to study a Machine that have Omron 3g3mv VFDs that is controlled by CJ1m CPU and SCU41-V1 communication card. The...
Replies
0
Views
455
Hello Guys, I have a Omron 3G3MX2 drive and I want to learn how its Modbus registers work by connecting to pc via Modbus poll software. does...
Replies
1
Views
678
Hello Guys, I have a packaging machine in the company that I work for that have 8 Omron VFDs (3G3MV ) that are controlled via Modbus with CJ1M...
Replies
1
Views
585
Hello Guys, I have a machine that have 8 Omron 3G3MV VFDs and I am looking to migrate to Omron 3G3MX2 drives. the existing network is half duplex...
Replies
0
Views
559
Back
Top Bottom