Can 5069-L33xx local rack be expanded?

skyfox

Lifetime Supporting Member
Join Date
Nov 2006
Location
CA
Posts
279
1768-L43 Local rack was expandable in to a 2nd Rack via an expansion cable. For an example;


PS ENET CPU I/O I/O I/O I/O [Expansion Cable] - Main Local Rack

PS I/O I/O I/O .... [END CAP] - Local Rack Expansion


Can the Same be done with 5069-L330xx series PLC's? I couldn't find any info that said it could or couldn't be done.


Thanks-
 
Don't think you can. At least if you put it into IAB and try to configure a second bank it won't let you like it lets 1769/1768 processors
 