I'm not 100% sure that I'm following everything that you're reporting -

but -

whenever an Allen-Bradley processor has a "go to run" experience - each OTE instruction will go write a ZERO into its bit box ... this is a part of the PRE-SCAN operation ...

if you'll look at it that way it will probably start to make sense ...

NOTE: it's a little more complicated than that for a ControlLogix or CompactLogix system - but we'll skip that part since you're not working with either of those platforms ...