Old December 14th, 2014, 08:47 PM   #7
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,387
Quote:
Originally Posted by Ron Beaufort View Post
thanks ... good to know that someone has my back ... I'm working on putting together a little "dog and pony" show for Safety I/O in my "home" lab and I don't multitask too well when I'm this tired ...



I may have to correct this in the morning but here's the general idea ...

first let's start with an SLC or MicroLogix system ...

suppose that you're using a LATCH (OTL) instruction and an UNLATCH (OTU) instruction and that both rungs are FALSE ...

suppose that the bit/box has a status of ONE when you shut down the system ...

when the system powers back up again (go to run) the bit/box should still have a ONE status ... it "retains" its status is how this operation is usually described ...

but suppose that you add another rung even an UNconditional rung with an OTE instruction for the same bit address and that you place this rung in an UNUSED subroutine ... specifically, the subroutine has NO way to be executed ... no JSR no STI no DII no "NUTHIN" to tell the processor to scan/execute the OTE rung ...

(some programmers create a "scrap pile" subroutine and "park" unused rungs in it just in case they might need them later) ...

now when you power down and back up or go to program mode and then back to run mode (go to run) the LATCH bit will NOT retain its ON status ... specifically, PRE-SCAN will find that "UNUSED" OTE instruction and go write a ZERO into the bit/box ...

now for a ControlLogix or CompactLogix system ...

suppose that we set up the same test as before ...

now when you power down and back up or go to program mode and then back to run mode (go to run) the LATCH bit WILL retain its ON status ... specifically, PRE-SCAN operation will NOT find and execute that "UNUSED" subroutine ...

now add a JSR rung to "call" the unused subroutines in each of the systems and make both of the JSR rungs FALSE ... for example: use an AFI instruction for the Control/CompactLogix JSR rung and maybe use just an XIC left in a ZERO status for the SLC/MicroLogix JSR rung ...

if my memory serves correctly the LATCHED bit/box in the Control/CompactLogix system will now be reset to OFF just like the SLC/MicroLogix ...

basic idea (again from memory) the Control/CompactLogix platform must have "someway" some "PATH" - to find and scan the subroutine on PRE-SCAN EVEN IF THAT PATH IS GUARANTEED TO BE FALSE ...

DISCLAIMER: I'm dong this by memory and don't have time to double-check it but I'd bet more than pocket change that I've got it right ...

closing out this type of thing is why I personally don't refer to "seal-in" rung constructions as "latched" rungs ... many people do that but there is a BIG difference between how actual LATCHED/UNLATCHED rungs operate and how "SEALED-IN" rungs operate ...

Wow ! that's a gotcha for sure - I must test this asap - great heads-up, Ron..
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote