Can someone explain precharge in a ac drive to me? How it works in detail and what it is used for?

Also how does it come into play in a common dc bus system.

I am configuring some drives here http://raise.rockwellautomation.com...cmd=edit&CID=9C53AE259194489992CEB2FB57E45F45

And i have a choice of ac/dc input without pre charge and dc input with precharge.

I would like to get the ac/dc version because it is off the shelf and i need this in a hurry. But do i need precharge in a common dc bus circuit? if so how do accomplish precharge outside the drive correctly?
 
In short, an AC Drive has a rectifier front end feeding a capacitor stack.
Without some sort of pre-charge circuit, you will generally destroy input components in short order on power up (and/or blow fuses, open breakers, etc).

The basic precharge circuitry usually is something as simple as a contactor that shorts out one or more resistors in series with the AC input after the capacitor bank has charged up to some safe amount. More advanced drives will have a phase controlled front end to do the same thing, and bring the capacitor bank charge up slowly.

Active Front End units for a DC Bus are almost always phase controlled, but they don't need to be. Again, they will ramp up the DC Link voltage slowly, as with a common buss system each drive probably still has local capacitance, or there might be capacitor modules in the system. Some drives (DC Input) will still have a pre-charge circuit, but not all of them.

In many cases here with Common buss systems, I take an output from the drive itself (buss up to voltage) to pilot an external DC Link contactor shorting out a pre-charge resistor. Without that, isolating a drive and reconnecting it to the buss would be an expensive experience from replacing the semiconductor fuses!
 
The system in question has a home brew rectifier ( no Precharge) which makes the dc bus and all the drives connect to it.

There is a chopper module connected to a single very large braking resisitor that shunts the voltage should it rise aboove 750 VDC.

All of the current drives have built in precharge and the replacemnts i was looking at does not so i am assuming i would need to change out the home brew rectifier for a powerflex rectifier unit with precharge sized for the system ( ie all drives)? What would be the method to size that?

Or use a system active front end vs using a rectifier unit?

Am i on the right path?
 
AFE's are definitely more expensive, but consider that usually they have the ability to regen power back to the source line, so you don't waste regen power as heat in a resistor.

Diodes are just that, a simple full wave rectifier, with or without a precharge circuit to reduce inrush surges on capacitor charges. These cannot be regenerative.

SCR Front ends also cannot USUALLY be regenerative, although there are some SCR Front end controllers that are. These have a built in precharge, based on phase controlling the input full wave SCR bridge to bring the buss up slowly.

If you are just putting new drives on an existing stupid buss, there is no reason not to roll your own precharge circuit; it's just a contactor (one pole will do) with a power resistor across the pole. On power up, the contactor is de-energized. Once the drive module reports that its buss is up to voltage (usually a configurable digital output), energize the contactor to short out the inrush-limiting resistor. Do make sure to interlock the contactor with the actual drive enable with an aux.
 
Bob

What formula would i use to size the power resistor correctly.

How do you determine the correct rate of charge or rate of allowed voltage rise on the buss?
 

Similar Topics

Hello all! New user as of a day ago, first post! Just wondering if anyone has ever purchased and / or knows where to purchase a pre-built PLC...
Replies
9
Views
2,851
I am working with a customer template who uses pre and post instructions in Graph. I have not used these before in Graph, and I am trying to...
Replies
3
Views
1,367
Hi Guys, What the quick and dirty way to load a PRE value to a counter in a ML1200 from a C-More HMI? Having trouble using the HMI to reset a...
Replies
2
Views
1,319
I am trying to figure out how to use the predefined AOI, cant seem to find it in the manual for the add on instructions. Any help out there on a...
Replies
1
Views
1,732
Hey guys- I have an array of 30 timers. I want to copy a # into all 30 of the .PRE registers. Can I use a copy instruction into Timer[0].Pre with...
Replies
24
Views
15,636
Back
Top Bottom