Failure to upload/go online, ControlLogix 5561

Jasondelane

Lifetime Supporting Member
Join Date
Mar 2015
Location
Florence sc
Posts
220
Hi everyone,

I've got a 1756-L61/B, 19.11, and RSLogix is failing to go online or upload to a new program. I have the program that was created from the aborted upload attached, but the old program that I attempted to go online with is too large. The new program does not list all the modules, which include controlnet, ethernet, hydraulic, DC Input, AC in and out, and two flex i/o in the operator consoles.

The error I'm getting is 806-8004280A, and the entire error log looks like:

Uploading project from controller 'Charles_Ingram_1257_18' into file Charles_Ingram_1257_18.ACD...
Preparing the Database...
Uploading all Data Types...
Uploading all Controller Tags...
Uploading Device, Extended Device, and Memory Objects...
Uploading all Add-On Instructions...
Uploading all Programs...
Uploading program 'MainProgram'
Uploading all 'MainProgram' Tags...
Uploading all 'MainProgram' Routines...
Uploading routine 'STI'
Uploading routine 'SKEW_TARGET'
Uploading routine 'WIDTH_AVG'
Uploading routine 'MMI_SCREENS'
Uploading routine 'SEQUENCERS'
Uploading routine 'LUG_SPEED'
Uploading routine 'MMI_MSGNUM'
Uploading routine 'EDGER_FEED'
Uploading routine 'RESAW'
Uploading routine 'HYD_GRADIENTS'
Uploading routine 'TALLY_DATA'
Uploading routine 'LUG_INLK'
Uploading routine 'TARGET_FETCHERS'
Uploading routine 'LUG_POSITION'
Uploading routine 'FEED_TABLE'
Uploading routine 'OILER_SYSTEMS'
Uploading routine 'HYD_FAULTS'
Uploading routine 'SKEW_INIT'
Uploading routine 'MODE_BITS'
Uploading routine 'SKEW_NEAREND_SECOND'
Uploading routine 'MOTORS'
Uploading routine 'MMI_DISPLAY'
Uploading routine 'MEASURE_SPEED'
Uploading routine 'LUG_DRIVE'
Uploading routine 'INFEED'
Uploading routine 'HYD_HYD100'
Uploading routine 'BIT_SHIFT'
Uploading routine 'PRESSROLLS'
Uploading routine 'WIDTH_COUNTS'
Uploading routine 'MINIMUM_CUT'
Uploading routine 'MISC_ITEMS'
Uploading routine 'MMI_CALIB'
Uploading routine 'PREPOS_DN'
Uploading routine 'HYD_JOG'
Uploading routine 'OFFSETS'
Uploading routine 'MAIN_ROUTINE'
Uploading routine 'FETCHER_OVERRIDE'
Uploading routine 'WIDEST_EYE'
Uploading routine 'HYD_MAIN'
Uploading routine 'CHANGE_SAWS'
Uploading routine 'MMI_MSGDET'
Uploading routine 'FETCH_HOME'
Uploading routine 'OPTIMIZER_DATA'
Uploading routine 'CAL_FAIL'
Uploading routine 'EDGER_INIT'
Uploading routine 'GRAPH_GAP'
Uploading routine 'MMI_OVERRIDES'
Uploading routine 'MMI_STATUS'
Uploading routine 'RESAW_DIVERTER'
Uploading routine 'BOARDS_ONE'
Uploading routine 'NEXT_BOARD'
Uploading routine 'HYD_POSITION'
Uploading routine 'SKEW_FAREND_FIRST'
Uploading routine 'HYD_CONTROLS'
Uploading routine 'PREPOS_UP'
Uploading routine 'TARGET_SAWS'
Uploading routine 'SKEW_END'
Uploading routine 'HYD_CALIB'
Uploading routine 'ELECTROCAM'
Uploading all Modules...
Error: No port was found with the given port number.
Error: Failed to upload modules.
Complete - 2 error(s), 0 warning(s)

It will tell me that RSLogix is being taken offline, and thats it.

I did notice that the old program has the controller revision as 19.52, which is different than what's coming up when I try to do an upload to a new program.

Any ideas on the steps I should take? I can't take the machine offline during the day, but we may be able to do it tonight. Do you think it'll upload in Program mode?
 
Ok, I've tried connecting through Ethernet and it's coming up on RSLinx, but I'm still getting the same error, No Port Was Found With the Given Port Number.

I made sure to add both the IP for the Ethernet module and the Ethernet "Optimizer" that is listed in the original program.

I read through the manual for the 19.052 firmware, but haven't found anything relevant to this problem.
 
Here are my RSLinx logs for when I was trying to upload.

04/15/15 13:44:07 12.57.18.1 Can't read port type: read from Harmony property bag failed
04/15/15 13:44:08 12.57.18.1 Attempting first connection, protocol = CSPv4
04/15/15 13:44:09 12.57.18.1 Unable to establish TCP connection to the Ethernet Interface
04/15/15 13:44:09 12.57.18.1 [10061] Connection refused
04/15/15 13:44:09 12.57.18.1 Device refused a CSPv4 connection, retry using EtherNet/IP
04/15/15 13:44:09 12.57.18.1 Attempting first connection, protocol = EtherNet/IP
04/15/15 13:44:09 12.57.18.1 Device has accepted the EtherNet/IP connection
04/15/15 13:50:46 12.57.18.1 Error receiving data from the Ethernet Interface
04/15/15 13:50:46 12.57.18.1 [10054] Connection reset by peer
04/15/15 13:50:46 12.57.18.1 EtherNet/IP connection has been lost
04/15/15 13:50:56 12.57.18.1 Attempting to reestablish a lost EtherNet/IP connection
04/15/15 13:50:56 12.57.18.1 Device has accepted the EtherNet/IP connection
04/15/15 14:01:52 12.57.18.2 Can't read port type: no Harmony port for this IP address
04/15/15 14:04:06 12.57.18.2 Attempting first connection, protocol = CSPv4
04/15/15 14:04:07 12.57.18.2 Unable to establish TCP connection to the Ethernet Interface
04/15/15 14:04:07 12.57.18.2 [10061] Connection refused
04/15/15 14:04:07 12.57.18.2 Device refused a CSPv4 connection, retry using EtherNet/IP
04/15/15 14:04:07 12.57.18.2 Attempting first connection, protocol = EtherNet/IP
04/15/15 14:04:07 12.57.18.2 Device has accepted the EtherNet/IP connection
04/15/15 14:04:07 12.57.18.2 Can't set port type to 288: no Harmony port for this IP address
 
I've read through that KB article, and it is asking me to upload or download, but when I choose to upload to a new file, it fails with the error I mentioned above.
 
If this is a redundant system, most likely the controller is secured.
This is the last "bullet point" of the RA Knowledgebase TechNote 676537 (Access Everyone- Link in Post #5)

"...RSL5K will not upload, download or go online with a secured controller. Unsecure the controller and try again...."
 
Also, it's got the redundant firmware, but the system isn't redundant. It's only got one controller, and redundancy is turned off. I've gone through every module on RSLinx and everything is setup for all users, no log on or pws, and I'm still getting the same error on upload.
 
For reasons that are unclear, RA added a leading zero to controller firmware revisions, but still allows many software products and user manuals to refer to the minor revision without the leading zero.

The ".5 and above" rule still applies to redundant firmware, which is why we know that 19.011 is nonredundant and 19.052 is redundant.

The offline file being set up for the wrong firmware revision might be an issue. You can experiment with just uploading into a new empty file rather than attempting to correlate with the old file.

The Harmony error may be getting conflated with the Module upload error. I would try doing a full reset of the RSLinx Classic drivers, as described in RA Knowledgebase article 39930 (TechConnect required).

You have my sympathy on that confusion; I just checked the firmware on a controller that a colleague set up but I have on a bench in my office. It's a single-controller, 4-slot application, and yet he loaded 20.054 firmware (for Redundant controllers).
 
Ken, I did an upload to an empty file to doublecheck, and it's saying the file is Revision .052, even though the controller isnt set up for redundancy. I'm still getting the error. I'm downloading all the ethernet EDS files just to get that out of the way and make sure RSLinx identifies all the modules. I'm running out of ideas.
 

Similar Topics

Hi guys, I am trying to upload the program but I am failure.i established communication between laptop and plc through RSlinx classic...
Replies
3
Views
2,399
I have a CNC cutting equipment, all the components are Fanuc from the CNC CPU A02B-0307-B822, a PLC AIF01A and a panel i, on the panel i (operator...
Replies
1
Views
45
Wizards, It has been a few, but you all have always done me well. I have acquired a 1769-L33ER and want to use it as my collection PLC to...
Replies
5
Views
463
Spoke to a few outlets including Emerson and some distributors. Apparently updating firmware on subsequent modules past the CPU still uses...
Replies
1
Views
349
Hello Everyone, i Have im my Industry a Endress & Hauser Promag400 this has a screen that constantly have that error, it says to wait, somebody...
Replies
2
Views
425
Back
Top Bottom