Hi,

Does anyone have any examples on how to use the Modbus IO Scanner on the Schneider M221 controller?

I have one on test bench with a Delta VFD-EL i want to control. I cannot get my head around how to set it up and communicate. The documentation isn't exactly easy from either Schneider or Delta.

Regards,

Beau
 
Hi,

1. Setup IP address of M221
2. Enable Modbus TCP IO Scanner
3. Setup Generic slave with IP address
4. Setup channels for the slave
5. You will see the IOScanner registers once the channels are setup
6. Use those registers to control your drive, check status etc.
7. For more information - SoM Basic help file -> Programming -> Network objects -> IOScanner objects

I have attached some pictures.
Also, you will need a minimum functional level of 6.0 to use the Modbus TCPIO Scanner.

If you are using Schneider ATV drives then we have pre-built function blocks to run the drives.

Hope this helps.
Thanks.

Slave_Setup.jpg IOScanner_Registers.jpg
 
Hello,

I have mine now working for Serial IO Scanning, getting data from an Access Point. Do you have any documentation or procedure on working with an M221 PLC and an Access Point connected to 10 devices possibly without IO Scanning?

Thanks!

Blevine
 

Similar Topics

Hi all, I've been trying to develop modbus rtu program between uv balasts and plc ı'have 6 slave balast.I am reading fault run voltages etc...
Replies
0
Views
1,172
Hi all, I have a HACH sc200 controller with 2 sensors which I hope to connect an M221 plc to via Modbus RS485 in order to display the info on a...
Replies
4
Views
2,239
Hi All, I am a newbie to Modbus tcp communication, and need some directions in this regard. I have TMCE221CE16R with SoMachine Basic as my...
Replies
9
Views
5,275
Hi all I tried to piggyback onto the back of an old thread, but I think I need to ask for help on here. I am trying to get two M221 plcs to...
Replies
5
Views
4,596
hello eveyrone I want to make an application with M221 PLC in SOMACHINE BASIC program. I request your valuable help. I have a 50 ms pulse...
Replies
1
Views
1,584
Back
Top Bottom