Make of plc

Never seen it before but suspect it is a clone of the Mitsubishi FX series there are many versions of them, main differences are limited functionality, 232 rather than 422/485 port.
 
The LEDs all look they show the status of the X (Inputs?) and Y (Outputs?) with nothing to show whether or not a program is running. That suggests the unit is just an I/O device as others have already pointed out. Follow the cable at the lower right. Most likely it leads to the CPU.
 
The LEDs all look they show the status of the X (Inputs?) and Y (Outputs?) with nothing to show whether or not a program is running. That suggests the unit is just an I/O device as others have already pointed out. Follow the cable at the lower right. Most likely it leads to the CPU.

the x and y are seemingly random.... 0-7 10-17, 20-27... but not in order.

30-32.... oops, because we skipped X8,x9, x18,x19, x28,x29 for some reason.... lol


and then they even skipped Y22 for no discernible reason at all... just one random "output" not listed or used, and out of order...

this screams copycat backline 4th shift overnight line running OPS in china.
 
I am betting that the HMI an integrated PLC/HMI, and the part shown in post #1 is an expansion for this PLC/HMI combo.
Search for Samkoon PLC you will find some images of devices that look similar if not identical.
 
This is the rear of a Samkoon PLC/HMI
Samkoon-4-3-inch-HMI-PLC-All-in-one-Integrated-controller-HMI-Touch-Screen-Panel-8DI.jpg_Q90.jpg_.webp

Notice the lettering of the terminals are in the same style.
 
a lot of the samkoon and aliexpress fakes use FX part numbers from real mitsubishi PLCs too. so if you see anything on this that says FX, then I think they're on to something with the samkoon software.
 
plc

no i/o on hmi so not extension, tried samkoon software no joy,hmi configured for modbus coms so no help
 

Similar Topics

Hi all smart and knowledgeable people.I have a hmi connected to 2 Plcs via ethernet.These 2 Plcs connected to control 2 systems in one machine...
Replies
2
Views
89
Hello, We are now working on a software to collet the configuration of different PLC brands ,using a third software to backup all the simens...
Replies
4
Views
72
Dear Experts, I've come across an unusual piece of hardware for AB PLC-5 racks. I mean the NT-1776-HSD-R resolver input module. I have tried...
Replies
0
Views
43
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
Replies
12
Views
232
Hello all. I recently had to re install my AutoCAD Electrical 2024. I am trying to find the Rockwell catalog to install in it but cant find...
Replies
0
Views
101
Back
Top Bottom