Dear all,
Good day,
Please i need your help as i have a condensate surge vessel and mounted on it two level transmitter(DP type).one for (HH and H alarm that make pump operating) and the other one for (L and LL alarm to make the pump stop). This vessel is containing condensate and above it blanket gas. My question is" what is the configuration of the two transmitter dry or wet leg?"
 
It depends.
~ is there a controller** that the two sensors are inputs to?
~ if not do the controllers have any "intelligence"?
~ is each alarm type a separate dry contact or solid state switxh?

** more information may be needed
 
I know the difference between them but i need to know condensate surge vessel used wet or dry leg from experience or from best practice
 
I would think that you want the high or wet leg on the bottom port, then the lo or dry leg on the top port.
 
I guess that would depend on your medium.

We measure level in hot water and steam boilers. Here both sides of the DP measurement will have water. The lower measures the actual level, the higher will fill up with condensate and be the reference point.
 
I would think that you want the high or wet leg on the bottom port, then the lo or dry leg on the top port.

In an open vessel, the low side of the DP transmitter may be open to atmosphere.

In a closed vessel, the low leg should be connected to the top port in the tank.

If the gasses that accumulate in the top of the vessel will condense and introduce fluid into the low side piping, then you must fill the piping with fluid and recalibrate the DP transmitter for "wet leg" operation. Otherwise, the fluid that accumulates in the low leg piping will create head pressure on the transmitter which introduces a measurement error.
 
In an open vessel, the low side of the DP transmitter may be open to atmosphere.

In a closed vessel, the low leg should be connected to the top port in the tank.

If the gasses that accumulate in the top of the vessel will condense and introduce fluid into the low side piping, then you must fill the piping with fluid and recalibrate the DP transmitter for "wet leg" operation. Otherwise, the fluid that accumulates in the low leg piping will create head pressure on the transmitter which introduces a measurement error.


Another option would be a condensate trap that is drained.
 
That strikes me as a more complex solution than simply using a wet leg on both sides of the transmitter. I'm a fan of the KISS Principle myself.

True. The only thing is that you would not have to rezero and span the transmitter (or figure out scaling taking into account specific gravity etc)
 

Similar Topics

Good Afternoon , We have been using Seal Shield Washable keyboards in the plant. These just don't last, and even after we buy a few, only...
Replies
3
Views
1,782
Hello. We had our fire suppression system trip last week (while we were snowed out of the plant), and it sprayed so much water that our PLC...
Replies
26
Views
5,842
Not sure if anyone works in this field or deals with these machines. Very high voltage (low amperes - 100mA or so). We are building a prototype...
Replies
1
Views
1,351
I am using a Siemens s7-300 PLC and need to add a second wet well level. Basically the system will utilize the primary wet well level...
Replies
6
Views
2,120
I am having trouble believing how complicated this is. I'm using CLX and I wish I could find some sample code or easier formulation to calculate...
Replies
15
Views
8,284
Back
Top Bottom