analog flexI/O to VFD

jcole28

Member
Join Date
Jan 2018
Location
Kentucky
Posts
8
View attachment vfdvfd.pdf

The attached files shows analog terminations from flex I/O modules to VFD. I have someone telling me that I should use isolated cards instead of nonisolated cards. I don't see any possibility of noise or ground loops. Why else would I use isolated over nonisolated? Am I missing something? Do you see a problem with the terminations? I am not familiar with flex I/O but it doesn't seem any different than any other analog modules that I have installed. There are also three 4-20mA devices connected to analog input card. The VFD is a 0-10v input. I don't see this being a reason to isolate though.
 
Last edited: