Fault & restart AB SLC 5/04 periodically
Ffakury
Feb 2014
Tehran
Hi
Any one know how i can clear this fault?
Cpu run led turn on for a second then red fault led turn on for a second then cpu restart and all leds turn off and on. This routine happened periodically.
I remove ram battery and clear cpu ram but problem not solved. In program mode when i switch to prog. Just fault led turn on for a second and cpu restart again . Because of the cpu restarting periodically i cant communicate with that .
I remove eeprom and power on cpu , just the fault led turn on steady and cpu not restart more.
If you can go online with the controller take a look at processor status- error tab and tell
us what the fault is (S:54) and its description.
Unfortantly periodically restart not allow me to communicate with cpu. And question is why cpu restart periodically and not steady fault!
One of the more common issues is a faulty power supply. If you have another
replace it. Also grounding issues, check a double check your processor ground.
Ok i will check ground , but do you have any documentation regarding pin configuration of cpu? My mean what pin is VCC or ground ?
And another issue is if power supply has problem why when i remove eeprom the cup goes to steady fault and not restart more?
Ffakury....
Power OFF - Put the keyswitch to the PROG position, and power ON - what happens? (LED states)
Remove the EEPROM module, and again power ON with keyswitch in PROG position - what happens?
See pdf
This procedure will clear the processors memory. Make sure you have a backup before doing this.
I switch to prog mode the fault led turn on one second and then cpu restart again . This happened periodically.
I remove eeprom and power on cpu the fault led turn on steady
So the SLC 5/04 PLC restarts with the EEPROM installed, but DOES NOT restart with the EEPROM removed? Most likely the S:1/10 bit is set in the Status file. That explains the restarting, but not what is the error.
I'm editing a program that has been in operation on my Rockwell Automation Mico850. The unit faulted while (re)downloading the program via...
2,493
Is there any way to restart CPU after runtime error has occured? We have a program with quite a lot of overflow bugs that we are currently...
1,570
Have a system that has been running for over a year and all of a sudden getting a ExcessiveVelocityFault on one of the drives when the MSO command...
132
Hi, Experts: We have 20 + years old GE PLC series 90-30 stop running (the run led not on and battery led not on) and HMI showing that "PLC has...
181
Power flex 527 Network based safety drive had faulty and alarm pop up SOS Code internal fault Unable to set or clear the fault manually or...
106
