I have a RS485 modbus network. I'm looking at an HMI and a modem as a masters, and I have a proprietary board as a slave.

Obviously we can't have 2 masters on the same network. So I was thinking of using a DPDT switch to switch between masters. RS485 is 2 wires, so have NO wired to 1 master, and the NC wired to the 2nd?

Thoughts?
 
Theoretically this it is possible. The system is not usually designed for two masters unless using Modbus TCP (Ethernet). You will have to stop the master that is not communicating to the slave. This may be hard to do.
Can the HMI or Modem be a slave as well?
Can your proprietary board have another Modbus communication port? (Set up another network)

Regards,
 
Theoretically this it is possible. The system is not usually designed for two masters unless using Modbus TCP (Ethernet). You will have to stop the master that is not communicating to the slave. This may be hard to do.
Can the HMI or Modem be a slave as well?
Can your proprietary board have another Modbus communication port? (Set up another network)

Regards,

I don't think the HMI or modem can be a slave. By definition they are polling for information. The proprietary board doesn't have another com port :(
 
In this situation I typically use an arbitrator (google scadalink ip100 for example) or an intermediate device (such as a scadapack) that polls the device and then the hosts poll it.
 
I've had success using DTDT relays to do exactly what you're wanting to do. I had only several devices that could only be on RS-232. Depending on how fast you need the data, it should work just fine
 
Use bifurcated gold plated contacts and it will probably work well. If you switch the relay mid-message you might get an error, but most devices will handle that fine and resume normal functioning.
 

Similar Topics

I need several DPDT switches to switch twisted pair, shielded RS485 comm cable between a PC (for setup) and the master (an HMI) I want to bury...
Replies
1
Views
4,911
Hi Guys, I have a Stratix 5700 managed switch that will connected to another different network thus: Stratix 1 on 10.50.3.xx >connect through...
Replies
0
Views
73
Good Afternoon , We all must of done this before ...... Installing a Frequency Drive in an enclosure , you forget how deep your selector...
Replies
1
Views
103
Hi all, I heard some cool things today regarding network switch diagnostics (i had usually always brushed over these without much thought.) I was...
Replies
0
Views
132
Hi all, First, thank you for reading the thread. So I had a task as the following: An up-counter must be programmed as part of a batch-counting...
Replies
7
Views
238
Back
Top Bottom