pressure transducer

jarvism

Member
Join Date
Jan 2017
Location
Graham
Posts
7
A little background info I work at a underground coal mine. We have a Dust tank capable of holding 135 tons of rock dust on the surface. We use this tank to drop dust underground. I have a issue we use Omega 0-50psi 4-20ma pressure transducers to calculate the remaining amount of dust in the tank. It feeds into a 1734 RIO with a 1734 IE4C analog card with a L32e processor. The issue I am having is my reading is fluctuating a lot. was trying to find ways of smoothing it out a little
 
you can try and average it over a minute. that should help reduce fluctuations. The time you average it over should be such that it doesn't impact a good reading.

what sort of fluctuations is it, only when certain things are on? ac line noise from nearby power can induce noise into the 4-20ma signal and cause erratic readings.
 
The best way would be to install load cells on the tank. they can be retrofitted in most cases. Lasers, ultrasonic, radar would not give you good results
 
First order filter can do a lot to help out and it's easy math. Load cells are ideal, but can be costly to implement on existing equipment. Emery Winslow makes great load cell system for all sorts of machinery, and their hydrostatic systems can weigh nearly anything.

Don't judge them by the website...either under construction or I found the wrong link.

http://ew.mbcsitedev.com/scale-type/tank-hopper/
 
A little background info I work at a underground coal mine. We have a Dust tank capable of holding 135 tons of rock dust on the surface. We use this tank to drop dust underground. I have a issue we use Omega 0-50psi 4-20ma pressure transducers to calculate the remaining amount of dust in the tank. It feeds into a 1734 RIO with a 1734 IE4C analog card with a L32e processor. The issue I am having is my reading is fluctuating a lot. was trying to find ways of smoothing it out a little


I agree with Nova5 if load cells are a non-starter.



How is pressure used to calculate the remaining dust in the tank? Is it a fluidized bed?
 
you said the magic word, dust.
so i have to ask you several things.
1. is the device going through an intrensic barrier and if so, what is it and the model number?
2. are you using the electrical installation requirements for class 2?
3. is the 4-20 ma signal shield connected at the plc side only?
4. is this signal near any high voltage motor wiring and if it is, is the motor cable shielded? is this a vfd motor?
i'm asking questions to help promote safety, and also answer your 4-20 ma issue.
james
 
Have you been using this method for a long time or is it a new installation? To me, this sounds like a misapplication of a pressure transducer. It depends the dust behaving like a liquid. But I presume the absolute accuracy of the measurement is less important than establishing a benchmark for when to dump the contents.
It might be enough to simply add a timer to delay dumping the tank until the pressure transducer signal has remained above the trigger level for the duration of the timer preset.
 
I am still not sure how level affects pressure, but Logix5k has the MAVE instruction, which may do what you want, depending on the level of fluctuation.
 
The first answer should not be a filter.
The first question I have is are you filtering process noise, transducer noise or wiring noise.What Steven mentions is process noise.

When the system isn't changing, neither should the transducer output. The process noise should be zero. I would first measure the output at the transducer with a scope and look for noise. If it is noisy there could be a problem with the power supply being noisy. I would then compare that to noise at the input to the analog card and look for differences to see if the noise was induced on the wires. The problem here is that if the plant is shut down the may be no noise induced on the wiring because none of the equipment that would induce noise is running. Also, the problem Steve mentioned wouldn't occur when the system isn't running. Given that all that checks out then I would consider filtering with low pass filter.








BTW guys, there are better filters than the low pass filter. Yes it is simple but for a little more effort one can implement a two pole Butterworth filter.
https://deltamotion.com/peter/Mathcad/Mathcad - Butterworth NG.pdf


Another question, if you are going to use a low pass filter have you ever considered putting a capacitor across the input?
 

Similar Topics

Good morning everybody, I hope you are very well. I share with you the information of the PLC LOGO! Siemens and expansions that we have...
Replies
4
Views
1,055
Has any used a ballistic pressure transducer with a PLC? I am not sure if it will capture the event that I need to use as a control. The device...
Replies
2
Views
1,060
I am updating controls on a leak tester, from a SLC 5/02 to Compact Logix. The SLC used a DDV instruction to help scale a differential pressure...
Replies
17
Views
4,272
Hi Guys, Is a typical transducer programmed to output its signal in intervals? Say every 10 seconds it would generate a signal via 4-20mA loop...
Replies
3
Views
1,634
Does anyone have any recommendations for a good reasonably priced 4-20mA transducer I can use with a VFD running a PID loop on a wastewater line...
Replies
9
Views
3,920
Back
Top Bottom