GE 90-30 w/ FANUC I/O Link A Addressing Issues
beaver_rrr
Nov 2014
MD
Hello!
I've been trying to mate my 90-30 chassis (CPU363 w/IC693BEM321) with FANUC Model A I/O Link Slave Module (AIF01A) in 5-slot chassis ABU05A.
I've got them communicating, and I can read DI from I/O Link slave's AID16D, and I can send DO to the slave's AOD16D, and the actual problem is this:
Every actual I/O module in ABU chassis slot seems to take 8 full bytes in slave module memory, so when %I reference address for slave 0 in BEM321 configuration is %I00033,
actual input address for AID16D slot 1 is %I33-48, and slot 2 is 97-112, slot 3 - 161-176, with slots after 3 unusable due to slave memory limit of 256 bits.
Output module seems to follow that pattern, but instead of using first 2 bytes of an 8-byte "word", it uses last 2, so with slave %Q reference at %Q00033,
16-bit output module in slot 1 would take %Q81-96, slot 2 - 145-160, etc.
I've tried swapping ABU05A for ABU10A, and two different AIF01A modules, it changed nothing.
I don't have another BEM321 on hands, but could buy it if that looks like incorrect behavior from master module.
I've spent hours digging through manuals trying to find if it is possible to configure BEM321 or AIF01A to behave correctly and use only 16 bits for 16-point I/O modules, to no avail, and decided to ask here.
I tested this I/O Link chassis with 16-MC CNC controller, and it worked with seemingly correct addressing, so I assume there is something that needs to be done w/ BEM module.
Help, please?
As far as I know, the BEM321 doesn't care what modules are present in the drop. It only expects to see the number of input and output points defined in the configuration. Does the first input from the input module in slot 2 show up as %I97 when you configure slave 0 as CN01 (96 inputs, 64 outputs)?
Do you have to do anything to configure the slave module? Model A I/O modules are the same card as 90-30 I/O modules. The only difference is the color of the plastic case. In a 90-30 if you don't download a hardware configuration file to the CPU, a slot with a discrete input module will self-configure as 32 points regardless of the number of points on the module actually present. Perhaps that's what is happening here except its using 64 points instead of 32.
I only know enough about the Fanuc CNC side of things to make me dangerous. I'll check my files to see if I can find a manual for the Model A slave module.
Yes, but these 96 inputs start at %I33, so 97-112 are in range of available addresses.
No, there is nothing I could find to be configurable, I/O Link Model A manual number is B-61813E and it's... scarce, at best.
I tested different slave types, and the only one not turning "Slave 0 configuration mismatch" error bit on is SLAVE256.
I have one GE Fanuc IC200PNS002-AC Versamax Network Interface Module and the fault red light is blinking and i have checked in manual it is...
252
Hi everyone, We are having Fanuc 16 i CNC system. I need to interface SMC ex260 SEN-1 ethernet valve module with the CNC . Does anyone know the...
371
hi. - Now I have some machine CNC use tech by GE fanuc ( CNC, PLC, servo... support by GE Fanuc). I want to replace system PLC GE 90-30 on this...
3,373
to download or Upload Data from and to PLC i need Proficy Machine Edition , right? so what for i can use Proficy Historian ?? and what is InfoLink...
3,774
Hello, i am using profibus as communication between plc and fanuc arm. I can easily send inputs from plc to arm, but i can't monitor any outputs...
68