I think the CIP Path for a 1756-L8 controller is simply "2, IP"

The 2 is for the Ethernet port on the front of the controller when used in Ring mode. If you split and use two IP interfaces, they are Ports 2 and 3.

The "1,0" is not necessary at the end of the CIP Path because the message goes directly to the L8, and does not need to go through a backplane port (1) and 1756 Slot number (0) to get to the CPU.